In other words, check your battery voltage under an actual load, one that will 
be higher amps than any charging sources - such as the panels - coming in.

As William noted, that is a pretty small battery bank for that size inverter 
and I would suspect they have been hyper-cycled.

..................................................................................................
Northern Arizona Wind & Sun - Electricity From The Sun Since 1979
Solar Discussion Forum: http://www.wind-sun.com/ForumVB/
..................................................................................................
  ----- Original Message ----- 
  From: William Miller 
  To: RE-wrenches 
  Sent: Thursday, October 01, 2009 8:36 PM
  Subject: Re: [RE-wrenches] FX2000 / Trojan battery question


  Friends:

  A "Low AC Volts" error is very typical for a cave in battery voltage under 
load.  I've reported in this forum before the propensity of Outback inverters 
to misreport error conditions.

  4 L-16s is a very small battery bank.  I would not be at all surprised if 
this was indeed a battery or related wiring problem.

  William Miller





  At 05:18 PM 10/1/2009, you wrote:

    Content-Type: multipart/related;
            boundary="----=_NextPart_000_016B_01CA42E1.ED2C51E0"
    Content-Language: en-us

    Tom,
     
    The L-16's are 6v. So, they all had to be in series to operate at 24v 
(FX2024 is a 24v inverter).
    Dave
     
    From: [email protected] 
[mailto:[email protected]] On Behalf Of The Office of 
Tom Duffy
    Sent: Thursday, October 01, 2009 8:53 PM
    To: 'RE-wrenches'
    Subject: Re: [RE-wrenches] FX2000 / Trojan battery question
     
    Bob
    On the other note: Were the L-16s in series or series/parallel? Also were 
the voltage readings and Hydrometer readings done on an active bank or "at 
rest" and what were the readings?
     
      Tom Duffy
      Systems Design Engineer

         [email protected]
           575-539-2111 X 301

----------------------------------------------------------------------------

    From: [email protected] 
[mailto:[email protected]] On Behalf Of robert ellison
    Sent: Thursday, October 01, 2009 5:40 PM
    To: RE-wrenches
    Subject: [RE-wrenches] FX2000 / Trojan battery question
     
    Just visited a site with a 04 version FX2024 The inverter is shutting down 
and showing "low AC output voltage" 
    It is hooked to 4 Trojan L-16 G batteries. When i arrived the voltage was 
23.8, the other day when i arrived it was 25.5 volts and shut down both times 
with the same error showing. There are 1050 watts of panels and an MX 60 on the 
battery bank also. In the past when the batteries went low it would show a low 
battery error, so i don't expect that is the problem. Loads are minimal
    Disconnecting the battery or starting the generator clears the error.
     
    When i called Outback i was told there was a $250.00 "out of warranty 
charge" as well as a retail of $1400 for the boards. She also insists it was 
probably a bad battery bank, or at least needing an eq charge. It just had one 
9 days ago. The hydrometer readings are all close and the voltages similar.
     
    Anyone run into this before and have any knowledge on this error? 
     
    On another note, has anyone had any Trojan L-16 G batteries with cell 
failures? The date code is J8 
    I have had 2 in the last year, one was under warranty and the last one out 
of warranty.
    Anyone else had this problem or am i just unlucky?
     
    Thanks,
    Bob



------------------------------------------------------------------------------


  _______________________________________________
  List sponsored by Home Power magazine

  List Address: [email protected]

  Options & settings:
  http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

  List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

  List rules & etiquette:
  www.re-wrenches.org/etiquette.htm

  Check out participant bios:
  www.members.re-wrenches.org

<<attachment: 4ce320d.jpg>>

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to