William,

I think that outdoor flex rated 60 degrees C is acceptable. So do thousands of 
contractors who install air conditioners on roofs. A few years ago there was 
discussion about requiring 90 degrees C flex on roofs.

Joel Davidson




________________________________
From: William Miller <[email protected]>
To: RE-wrenches <[email protected]>
Sent: Mon, November 30, 2009 10:04:10 AM
Subject: Re: [RE-wrenches] wiring the Soladeck

Joel:

I have looked on the Carlon web site and the only temperature rating listed is 
for minimum temperatures.

Others had expressed this concern in that past.  The question arises as to how 
hot is it under a PV array and at what rate does the temperature reduce as one 
moves away from the back of the modules?  Our installations run NMLT along rack 
members but not against the backs of the modules.

If NMLT is not suitable as protection under a PV array, what do you suggest we 
use?

William Miller



At 05:52 PM 11/25/2009, you wrote:

Hello William,
>Nice under-array wiring. Are you using 90 degrees C. flex?
>Best regards,
>Joel Davidson