The water pipe should already be grounded to the grounding electrode system. If you connect to that system anywhere, you should be bonded to metallic water pipes, in a properly constructed electrical system.

At 12:21 AM 1/7/2010, you wrote:

My understanding is that if the water pipe is ferrous metal for a certain length into the soil - I think 10 or 15 ft. - then it is an NEC compliant grounding electrode.

Not the easiest thing to confirm on a retrofit. If we can't find an existing ground-rod we drive one ourselves.


Andrew Truitt
Standard Solar Inc.




Drake Chamberlin
Athens Electric
OH License 44810
CO License 3773
NABCEP TM  Certified PV Installer
Office - 740-448-7328
Mobile - 740-856-9648  