Ryan,

Metallic water pipes are supposed to be grounded; but not relied on as a grounding electrode.  So don't try to ground the solar system to the water pipe because it is supposed to be connected to a grounding electrode.  It should be okay to rely on building steel as the grounding electrode; unless local code or the inspector disallow it.

Kent Osterberg
Blue Mountain Solar, Inc.


Ryan LeBlanc wrote:
Thanks guys,

Follow up:

When providing a three-line drawing, in New York, on a new construction, few
story building, which means they'll have a ground rod (hopefully) at the
Main cabinet, do you think it's necessary to detail any ground connections
from the solar to the water pipes?  No right?  (Unusual inspector)

They are totally different systems when there is a Grounding Electrode
present.  In modern construction practices, they are bonding the water pipes
only, not using the water pipes as any part of the grounding electrode
system and therefore don't come into play?

And then, If on top of this building, there was a Satcon inverter, on the
roof, and that Satcon was getting grounded to the structural, can I run just
one ground wire to the roof, or do I need to run a ground conductor and some
kind of bond wire?  And again, the water pipes are not involved here, at
all.

With appreciation,

Ryan J. LeBlanc
NABCEPT Certified Solar PV Installer
Cell: 707.591.1950
Direct: 707.536.9839
[email protected]
http://www.NaturalEnergyWorks.com


_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

  

No virus found in this incoming message. Checked by AVG - www.avg.com Version: 9.0.725 / Virus Database: 270.14.127/2603 - Release Date: 01/05/10 23:35:00
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to