P.S.

In many cases it would be necessary to use a fused AC disconnect to stay within the inverter manufacturer's specifications.

At 12:53 PM 1/13/2010, you wrote:
Here is a wild idea. If you look at the Enphase inverter systems, several inverters connect together in parallel before going to an overcurrent device.

In all cases, the point of connection to a utility system must be at a dedicated breaker. If there were multiple string inverters that would connect to one breaker, why not just use a junction box, instead of a combiner panel? You could put in an AC disconnect for each inverter, if it didn't come with one.

The wiring would need to be sized for the combined output of the multiple inverters, which in many cases wouldn't be an issue.

Drake

Drake Chamberlin
Athens Electric
OH License 44810
CO License 3773
NABCEP TM  Certified PV Installer
Office - 740-448-7328
Mobile - 740-856-9648  