Kirk,

 

Disconnects within sight of combiner boxes will be required in 2011. Another
good reason to keep combiner boxes off residential rooftops. This is
targeting commercial rooftops where large system have no disconnects for
servicing fuses.


Bill.

 

From: [email protected]
[mailto:[email protected]] On Behalf Of Kirk
Herander, VSE
Sent: Wednesday, January 13, 2010 2:33 PM
To: 'RE-wrenches'
Subject: [RE-wrenches] 2011 code and roof discos

 

On that note Bill, will roof disconnects be required in the 2011 NEC?

 

Kirk Herander

Vermont Solar Engineering

802.863.1202

NABCEP(tm) Certified Solar Installer

NYSERDA-eligible Installer

VT Solar Incentive Program Partner

  _____  

From: [email protected]
[mailto:[email protected]] On Behalf Of Bill Brooks
Sent: Wednesday, January 13, 2010 12:36 AM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] Solar accumulation panel

 

Andrew,

 

It does not exist. We tried like crazy to get it into the 2011 NEC, but to
no avail. At the last second the proposal was put on hold until the 2014
NEC. Major bummer. For now it can only be done with AHJ approval. Many allow
it but it is not in the NEC. Alternatively you must use the sum of supply
breakers no greater than 120%. Much more restrictive.

 

Bill.

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to