Hi Chris, 

Fairly similar across the range. 

Regards, 

Jamie

>>> "Chris Worcester" <[email protected]> 1/13/2010 4:14 PM >>>

Hi Jamie, 
How do these values correlate to the larger Rolls batteries? We have a
number of the 2-KS-33’s out there along with other various sized large
Rolls battery banks. 
   

Sincerely,

Chris Worcester 
Solar Wind Works
NABCEP Certified PV Installer
Phone: 530-582-4503
Fax: 530-582-4603
www.solarwindworks.com
[email protected]
"Proven Energy Solutions" 

   

From:[email protected]
[mailto:[email protected]] On Behalf Of James
Surrette
Sent: Wednesday, January 13, 2010 11:43 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] discharging Rolls batteries 

  
Hi Hugh & Wrenches, 
  
Regarding the charge voltages you sited, you've got the gist. 
  
As battery temperature drops, you need to increase the charge voltage
to properly charge and, conversely, as temperatures rise, voltage needs
to be decreased to reduce the risk of overcharging. 
  
I believe the range we site to accommodate for temperature is (in C); 
  
0-16C: 2.5VPC 
17-27C: 2.4VPC 
28-40C: 2.36VPC 
  
These are your max bulk / absorb voltage settings. 
  
Regarding a low voltage disconnect, there is a significant difference
between on load and at rest voltages at 50% SOC. 
  
Below is a table of a cell being discharged at a known constant load
(C/20) over time at 25C; 
  
SOC        VPC 
100%       2.1 
75%         2.01 
50%         1.93 
25%        1.84 
0%          1.75 
  
Please note, this is for a cell(s) under constant load and at 25C.  If
the load increased, you would see lower voltages more quickly, 
Moreover, once the load is removed, resting voltages will increase
dramatically, i.e. 1.75VPC on load will equal ~1.95VPC at rest.  If you
were using 2.0VPC (on load) as your cut off, you would only have been
able to discharge ~25% - which does not include capacity reduction due
to temps <25C.......and I know they are lower than that here! 
  
Hope this is of some assistance. 
  
Regards, 
  
Jamie 




James Surrette

Surrette Battery Co. Ltd
1 Station Rd.
Springhill, NS, CAN
B0M 1X0

Direct: 902.597.4027
Fax: 902.597.8447




>>> Hugh <[email protected]> 1/13/2010 2:26 PM >>> 
Hi wrenches, 
  
I have been selling and using a few sets of Rolls 4000 series S530 
batteries lately. 
  
I have downloaded the Solar Battery manual from www.rollsbattery.com 
  
It's very interesting.  At 17 degrees C you need to charge at 14.4 
volts.  At 16 degrees it's 15 volts.  Hmm, Ok I get the idea.  I am 
certainly learning to compensate my temperatures this winter. 
  
I did a search in the document for the word 'discharge'.  I am 
cutting off at just below nominal voltage and starting my generator. 
I do not get much capacity.  A customer has suggested that a lot of 
the discharge capacity is to be had at 11.5 volts (he has a 12v 
system obviously).  Hmm.  Sounds a bit harsh.  But what voltage 
should I be considering to be 50% discharged, and time to start the 
genny?  And in a hard frost, the same voltage? 
  
No mention of discharge in the solar battery manual.  Any ideas anyone?

  
Please don't tell me to buy an amphour meter (or worse still to sell 
them).  Those things are way too confusing to calibrate.   I can tell 
you that I am not getting many amphours out of my batteries in these 
low temperatures before the voltage per cell drops below 2. 
  
What do I tell my customers about the end-of-discharge voltage for 
sustainable cycling of their Rolls batteries?  And is it temp 
compensated? 
  
thanks 
-- 
Hugh Piggott 
  
Scoraig Wind Electric 
Scotland 
http://www.scoraigwind.co.uk 
_______________________________________________ 
List sponsored by Home Power magazine 
  
List Address: [email protected] 
  
Options & settings: 
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
  
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

  
List rules & etiquette: 
www.re-wrenches.org/etiquette.htm 
  
Check out participant bios: 
www.members.re-wrenches.org 





This email and its attachments have been scanned by iConnection E-Mail
Firewall for viruses, spam, and malicious content.

The information transmitted in this email is intended only for the
entity or person to which it is addressed and may contain
confidential/privileged material. If you received this in error, please
contact the sender and delete the material from any computer. Any
review, retransmission, dissemination, or other use of this information
by persons or entities other than the intended recipient is strictly
prohibited. %^^% 
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to