Re: [RE-wrenches] discharging Rolls batteriesHi Hugh.

Positive electrode:  PbO2 + 3H +HSO4 + 2e = PbSO4 + 2H2O  (e= electron)

Negative electrode:  Pb + HSO4 = PbSO4 + H +2e

Sorry, I can't insert the superscript symbols to show electrical charge.  If it 
is confusing let me know and I will repost this with the charge in brackets 
following the ion.

In cold conditions the ion transfer rate slows so in effect the internal 
resistance of the cell rises.  It simply can't deliver the electrons under 
load.  If the electrons are taken out at a reduced rate then the Vdrop of the 
"internal resistance" is lowered and the cell terminal voltage stays up for 
longer.

So, to use your analogy of the bank, in cold weather the money counters operate 
more slowly and if the temperature rises they return to normal speed.  The 
money is still there, it is just the rate at which it comes out that varies.  
In cold weather the counters simply won't deliver as much before they say "my 
fingers are too cold, that's all you get today!"

Bruce Geddes
PowerOn
  ----- Original Message ----- 
  From: Hugh 
  To: RE-wrenches 
  Sent: Saturday, January 16, 2010 12:25 PM
  Subject: Re: [RE-wrenches] discharging Rolls batteries


  hi


  We know that batteries deliver less amphours at low temperature and at high 
currents.  Volts drop quicker.  That's my starting point.  My question that I 
still do not hear an answer to is this:


  If the battery is a bank account and its harder to get the money out in cold 
weather and when you want to get your hands on a lot at once...  Does this 
actually mean that some of the money gets lost?  What happens to it?  Is it 
perhaps available later when the bank warms up or the demand gets less hectic?  
Is there really less money in there or does it just seem like less due to the 
conditions?


  I notice that Ah capacity is actually defined as how much Amphours you can 
get out before the battery reaches a certain terminal voltage.  I am wondering 
whether it is the ability to maintain voltage that is the limiting factor 
whereas the chemicals in there can still deliver amphours, given  the right 
temperature and time later.  You can certainly see recovery take place when a 
battery warms up and/or operates on lighter loads.


  One last time what happens to the chemicals (lead and lead oxide) that 
represent Amphours of charge in the battery plates?  For me this is a little 
bit like current of 10 amps entering one end of  a piece of wire and only 9 
amps coming out the other end.  I understand that the volts go down due to 
voltage drop (in this analogy) but loss of current is entirely a different 
matter.


  Thanks for any help with this rather obscure question.


  Hugh


    A lead-acid battery is an electro-chemical processor (just like you and 
other living things). When you and your battery are cold or hot, performance 
changes because the chemical process is affected by temperature. Cold equals 
sluggish chemical reaction, reduces the capacity to perform work, and affects 
battery performance linearly. Battery chemistry is well understood. When I get 
some time, I'll google for temperature-based formulas and charts unless someone 
else posts the links first.

      ----- Original Message -----
      From: Hugh
      To: RE-wrenches
      Sent: Friday, January 15, 2010 12:02 AM
      Subject: Re: [RE-wrenches] discharging Rolls batteries


      Hi Jamie,




        Remember, as batteries cool actual capacity is reduced, so if 200AH is 
50% @ 25C it is significantly more than 50% @ 5C.   Thus, you are discharging 
more deeply.



      But earlier you put it this way:


          Regarding temperature effects on capacity, earlier responses are spot 
on as the lower capacity is totally as a result of slower reaction times as a 
result of lower temperatures.  



      There is an issue here that I need to understand better.  You state that 
a battery has lower capacity in low temperatures.  Suppose you take a fully 
charged, 400 Ah battery and cool it down to -5 degrees C where according to our 
numbers it will only have 80% of its nominal capacity.  You then remove 160 Ah 
(say 10 amps for 16 hours).  It will then be 50% discharged.  Now warm it up 
again to 20 degrees or whatever.  My question is: will you only have 200 
amphours left in it now?  And if so, what happened to the other 40 amphours?  
Does low temperature operation actually lose amphours, or is it just more 
sluggish?  What is the chemical explanation for the lost amphours?


      I understand batteries as a chemical process of converting amphours into 
chemical changes.  I assume that a given amount of electrical charge converts a 
given amount of lead into lead sulphate (and likewise) back again.  I 
understand that cooling will make this process less efficient and thereby 
result in a rise in charging voltage and a drop in discharging voltage.  But 
does a low temperature actually mean that a given amount of lead being 
converted to sulphate actually give you less amphours electrically?


      (I have similar questions in relation to Peukert's equation where high 
discharge rates impact on the amphour capacity.  The capacity apparently 
'recovers' when the discharge rate is reduced.  To what extent is the capacity 
actually lost by using high discharge rates and to what extent is it just a 
voltage effect that impacts on the terminal voltage, rather than the actual 
chemical state of the battery?)


      I hope you can follow my descriptions.
      --
      Hugh Piggott

      Scoraig Wind Electric
      Scotland
      http://www.scoraigwind.co.uk


--------------------------------------------------------------------------

      _______________________________________________
      List sponsored by Home Power magazine

      List Address: [email protected]

      Options & settings:
      http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

      List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

      List rules & etiquette:
      www.re-wrenches.org/etiquette.htm

      Check out participant bios:
      www.members.re-wrenches.org


    _______________________________________________
    List sponsored by Home Power magazine

    List Address: [email protected]

    Options & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm

    Check out participant bios:
    www.members.re-wrenches.org




-- 
Hugh Piggott

  Scoraig Wind Electric
  Scotland
  http://www.scoraigwind.co.uk


------------------------------------------------------------------------------


  _______________________________________________
  List sponsored by Home Power magazine

  List Address: [email protected]

  Options & settings:
  http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

  List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

  List rules & etiquette:
  www.re-wrenches.org/etiquette.htm

  Check out participant bios:
  www.members.re-wrenches.org

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to