Here is a repost of this information from 20067

Todd


Ok, I called Jake and he forwardedme to Brent Carper (253-395-6818) who works 
in the Puget Sound Energymetering department. I had a long conversation with 
him about how tometer battery based, grid tied inverters. 

The form 12s meter (recommended by Outback) is designed for 120/208 3phase so 
it is expecting to see 120º of phase difference between thetwo legs rather than 
180º,and being analog meters use the same core for both meter coils, thephysics 
of this would suggest even an analog meter will not accuratelyread net power 
produced (but it will probably be only 1 or 2% off). 

The best way to accomplish this is with a digital, form 12s meter. Now,not any 
old form 12s meter will work (sigh). These meters come in threevarieties: 

1- The most common default configuration is cumulative read. This will NOTwork. 
2- The other two configurations are net register or 
3- dual register


Both of these (2 & 3 above) will work, although net register willdo the 
calculations for you and dual register (sometimes called dualfunction) will 
leave you with separate buy and sell totals that willneed to be manually added 
together at the end of each billing cycle.

As far as I now know this is accurate information, but I have severalmeters 
coming that I am going to test out to confirm the above details.Hopefully 
Outback will annotate this on their "green tag meter" pdf.

[http://www.outbackpower.com/pdfs_general/Form%2012S%20Green-Tag%20meter.pdf] 
http://www.outbackpower.com/pdfs_general/Form%2012S%20Green-Tag%20meter.pdf

Todd



Ian Woofenden, Home Power wrote:
  
Hi Randy and Todd,  
  
Andy has actually changed jobs, and the new contact at PSE is:  
  
  Jake Wade  [mailto:[email protected]] <[email protected]>    
Green Power Program Implementer    
425-462-3459    
    
Best,  
  
Ian  
  
  Todd,    
    
The latest contact I have for Puget Sound Energy, RE program, is:    
    
Andy Hemstreet    
Program Implementer,    
Renewables and Green Power    
Puget Sound Energy    
Office - 425 456-2633    
[mailto:[email protected]] [email protected]    
    
Randy Brooks    
Brooks Solar, Inc.    
Solar Power for People    
140 Columbia View    
Chelan, WA  98816    
509-682-9646    
[mailto:[email protected]] [email protected]    
[http://www.brookssolar.com/] www.BrooksSolar.com    
    
On Jun 30, 2007, at 8:58 AM, Todd Cory, Mt. Shasta Energy Serviceswrote:    
    
    
Kelly and others interested in this,      
      
Yes form 12s meters and sockets have 5 terminals.      
      
I am going to do some more testing on this next week, but it appears      
only analog meters will work with the Outback directions. If you wantto      
use a digital meter, it needs to be configured to "net register". This      
should be clarified on the Outback green tag metering diagram.      
      
Who is your contact at PSE? I'd like to ask them what kind of"tweaking"      
they do to get the digital meters to work correctly.      
      
Todd      
      
      
Randy Brooks wrote:      
      
        
Todd,        
        
One thing the OutBack diagram does not mention is that the meter base        
requires an additional neutral socket for the 5th meter leg.  If you        
meter base does not have one, that may be the problem.  You can get a        
5th socket adapter for your meter base from the meter supplier too.        
        
take care,        
        
Randy Brooks        
Brooks Solar, Inc.        
Solar Power for People        
140 Columbia View        
Chelan, WA  98816        
509-682-9646        
[mailto:[email protected]] [email protected]        


On Thursday, January 28, 2010 12:57pm, [email protected] said:


 I am using an analog GE kwh meter on an outback system with battery backup to 
a protected loads panel.  The AC in to the inverter is attached to the bottom 
of one leg of the meter and the AC out of the inverter is connected to the top 
of the other leg. This should give me an accurate record of just the production 
from the system. The idea is that the AC IN that will power the protected loads 
panel at night will come in the bottom of one leg and turn the meter backwards 
then exit through the top of the meter going forward thus cancelling those kwh. 
out. I have a neutral hooked to the meter because I am using it to record 120V 
but I am not getting accurate readings with this configuration. Any suggestions 
on metering in this case? I need a utility grade kwh meter.  
 
Gary Easton
NABCEP Certified Solar PV
NABCEP Certified Solar Thermal 
APPALACHIAN RENEWABLE POWER LTD.
Stewart, Ohio 
740-277-8498

“I'd put my money on solar energy… I hope we don't have to wait 'til oil and 
coal run out before we tackle that.”

—Thomas Edison, in conversation with Henry Ford and Harvey Firestone, March 1931


_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to