We usually figure that (for example) in a 2-string bank, that one conductor 
could carry 2/3 of the current if the batteries are unbalanced for some reason. 
In other words, rather than cutting the amperage rating in half, we cut it by 
about 1/3. For 3 banks would cut it by 1/2, etc.

Probably not ideal in theory, as in a worst case scenario you could have one 
totally failed bank, but on the other hand selling the customer on a full array 
of expensive 4/0 jumpers is not always an easy thing to do. In fact if someone 
is using that much battery, they should probably be using a 24 or 48 volt 
system.

..................................................................................................
Northern Arizona Wind & Sun - Electricity From The Sun Since 1979
Solar Discussion Forum: http://www.wind-sun.com/ForumVB/
..................................................................................................
  ----- Original Message ----- 
  From: Allan Sindelar 
  To: RE-wrenches 
  Sent: Friday, February 19, 2010 10:03 PM
  Subject: Re: [RE-wrenches] single string of batts: must the interconnects be 
inverter size cables?


  Phil,
  Given the scenario that Mick presented, your advice is sound, and I'd do as 
you suggest. But by changing the scenario just a bit, it brings up a separate 
but related issue. 

  Mick's scenario describes two 12V batteries in series, or a single string. In 
that case all current flows through the one string, so a series interconnect 
would need to be sized equal to the battery cables, in this case 4/0. But if 
there were two (or more) parallel strings, would the same size requirement 
apply? That is, if a battery bank had two strings, in theory each would carry 
180 max amps (your example, 8,000/22, shared by 2 strings), which is within the 
ampacity of 2/0 interconnects. In reality, this only applies if current is 
equally spread among strings. Is it? 

  It seems to me that a properly wired and torqued set will split current paths 
equally until a cell fails, either prematurely or when the set approaches end 
of life. If there are three strings, then failure of one cell/string in this 
example would still not exceed ampacity on the remaining 2/0 strings.

  As with many issues, the goal is to find a balance between safety and 
performance versus cost and worst-case accommodation. I will always use 4/0 
with one cell string and a 250A breaker, but I have never seen a real-world 
problem using 2/0 interconnects, both series and parallel, with 2 or more 
strings. Phil, what do you say? Others?


  <![endif]--> 
  Allan Sindelar
  [email protected]
  NABCEP Certified Photovoltaic Installer
  EE98J Journeyman Electrician
  Positive Energy, Inc.
  3201 Calle Marie
  Santa Fe, New Mexico 87507
  505 424-1112
  www.positiveenergysolar.com



  Phil Undercuffler wrote: 
    The interconnects are part of the circuit.  Typical flexible cables used 
with batteries are THW rated (75C column), so in free air 2/0 interconnects 
would be good for 265 amps, before any temperature derates.  Therefore, you'd 
be safe from a NEC point of view.  However, if the inverter manufacturer has 
recommended 4/0 cables, then that recommendation would apply to all cables in 
the circuit.  Battery based inverters are asked to surge many times their rated 
capacity -- a 24V 4kW inverter surging to 2x capacity (pretty normal 
circumstances) is going to draw over 360 amps (8,000 / 22), even if only for a 
short period of time.  You don't want your interconnects to be the weak link in 
the system, causing shutdowns due to undervoltage unnecessarily.  

    I'd use 4/0.

    Phil Undercuffler
    Conergy






    On Fri, Feb 19, 2010 at 12:01 PM, Mick Abraham <[email protected]> 
wrote:

      Example: 12 two volt battery cells in one 24 volt string. 4kW 
inverter/charger has 250 amp DC breaker size and 4/0 cables...as the inverter 
folks would want.

      So...do the "cell to cell" interconnect cables have to also be 4/0? In 
the example above, 2/0 interconnects would suffice from the standpoint of basic 
safety...and even from the voltage drop standpoint...right?

      Inverter company people may be best qualified to answer this, but any 
replies will be appreciated. While I'm at it: do the inverter folks request 
oversize cables because they want more capacitance on the DC input...or what?

      Jolliness,

      Mick Abraham, Proprietor
      www.abrahamsolar.com

      Voice: 970-731-4675

      _______________________________________________
      List sponsored by Home Power magazine

      List Address: [email protected]

      Options & settings:
      http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

      List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

      List rules & etiquette:
      www.re-wrenches.org/etiquette.htm

      Check out participant bios:
      www.members.re-wrenches.org





----------------------------------------------------------------------------
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

  

------------------------------------------------------------------------------


  _______________________________________________
  List sponsored by Home Power magazine

  List Address: [email protected]

  Options & settings:
  http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

  List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

  List rules & etiquette:
  www.re-wrenches.org/etiquette.htm

  Check out participant bios:
  www.members.re-wrenches.org

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to