Hi Allan;

I with you, I normally downsize the interconnects in parallel strings to 2/0, 
but keep them the same as the main cables on anything that carries full 
current, as Phil made clear.
On golf cart batteries for instance, two 4/0 parallel lugs won't fit under one 
battery post, now that most manus shortened their posts. Also 4/0 cables can 
really strain those posts; I saw a couple of systems with 4/0 THHN used (NEC 
compliant) but the lead post ripped off the battery after several years from 
the bend put on the cable (creating a much more dangerous and unfused problem 
BTW)
Some of the sealed battery manus (B&B for instance) give max current output vs 
time charts, and that not only gives you something for cable sizing, but also 
is an eye opener, when expecting a single string of two 12 volt batteries to 
run a 4 Kw inverter. A battery that can only produce 250 amps for less than 5 
sec, doesn't deserve a cable sized for 24 hr continuous at that output.

R. Walters
[email protected]
Solar Engineer




On Feb 19, 2010, at 10:03 PM, Allan Sindelar wrote:

> Phil,
> Given the scenario that Mick presented, your advice is sound, and I'd do as 
> you suggest. But by changing the scenario just a bit, it brings up a separate 
> but related issue. 
> 
> Mick's scenario describes two 12V batteries in series, or a single string. In 
> that case all current flows through the one string, so a series interconnect 
> would need to be sized equal to the battery cables, in this case 4/0. But if 
> there were two (or more) parallel strings, would the same size requirement 
> apply? That is, if a battery bank had two strings, in theory each would carry 
> 180 max amps (your example, 8,000/22, shared by 2 strings), which is within 
> the ampacity of 2/0 interconnects. In reality, this only applies if current 
> is equally spread among strings. Is it? 
> 
> It seems to me that a properly wired and torqued set will split current paths 
> equally until a cell fails, either prematurely or when the set approaches end 
> of life. If there are three strings, then failure of one cell/string in this 
> example would still not exceed ampacity on the remaining 2/0 strings.
> 
> As with many issues, the goal is to find a balance between safety and 
> performance versus cost and worst-case accommodation. I will always use 4/0 
> with one cell string and a 250A breaker, but I have never seen a real-world 
> problem using 2/0 interconnects, both series and parallel, with 2 or more 
> strings. Phil, what do you say? Others?
> 
> Allan Sindelar
> [email protected]
> NABCEP Certified Photovoltaic Installer
> EE98J Journeyman Electrician
> Positive Energy, Inc.
> 3201 Calle Marie
> Santa Fe, New Mexico 87507
> 505 424-1112
> www.positiveenergysolar.com
> 
> 
> Phil Undercuffler wrote:
>> 
>> The interconnects are part of the circuit.  Typical flexible cables used 
>> with batteries are THW rated (75C column), so in free air 2/0 interconnects 
>> would be good for 265 amps, before any temperature derates.  Therefore, 
>> you'd be safe from a NEC point of view.  However, if the inverter 
>> manufacturer has recommended 4/0 cables, then that recommendation would 
>> apply to all cables in the circuit.  Battery based inverters are asked to 
>> surge many times their rated capacity -- a 24V 4kW inverter surging to 2x 
>> capacity (pretty normal circumstances) is going to draw over 360 amps (8,000 
>> / 22), even if only for a short period of time.  You don't want your 
>> interconnects to be the weak link in the system, causing shutdowns due to 
>> undervoltage unnecessarily.  
>> 
>> I'd use 4/0.
>> 
>> Phil Undercuffler
>> Conergy
>> 
>> 
>> 
>> 
>> 
>> On Fri, Feb 19, 2010 at 12:01 PM, Mick Abraham <[email protected]> wrote:
>> Example: 12 two volt battery cells in one 24 volt string. 4kW 
>> inverter/charger has 250 amp DC breaker size and 4/0 cables...as the 
>> inverter folks would want.
>> 
>> So...do the "cell to cell" interconnect cables have to also be 4/0? In the 
>> example above, 2/0 interconnects would suffice from the standpoint of basic 
>> safety...and even from the voltage drop standpoint...right?
>> 
>> Inverter company people may be best qualified to answer this, but any 
>> replies will be appreciated. While I'm at it: do the inverter folks request 
>> oversize cables because they want more capacitance on the DC input...or what?
>> 
>> Jolliness,
>> 
>> Mick Abraham, Proprietor
>> www.abrahamsolar.com
>> 
>> Voice: 970-731-4675
>> 
>> _______________________________________________
>> List sponsored by Home Power magazine
>> 
>> List Address: [email protected]
>> 
>> Options & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> List-Archive: 
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> 
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> 
>> Check out participant bios:
>> www.members.re-wrenches.org
>> 
>> 
>> 
>> 
>> _______________________________________________
>> List sponsored by Home Power magazine
>> 
>> List Address: [email protected]
>> 
>> Options & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> List-Archive: 
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> 
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> 
>> Check out participant bios:
>> www.members.re-wrenches.org
>> 
>>   
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: [email protected]
> 
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to