Sometimes utilities will set a max too- here in Florida the investor-owned utilities have a rule that you take (d...@stc) x 0.85 to get the "AC equivalent" size of the array. That size then can't exceed 90% of the service rating. Not sure if this is an issue in other states.

Scott McCalmont wrote:
Going all the way up to the rating of the service might not be such a
good idea. The utility may use smaller wires for the service drop than
you would expect based on the ampacity tables in the NEC. Considering
the example of a 400 A service:

- PG&E (local utility) requires 350 kcmil Aluminum conductors.
- Table 310.17 rates 350 kcmil Aluminum for 395 amps before temperature
correction.

With load diversity the smaller wires will be fine, but the output of a
PV system is continuous. Running the output of a system sized at 400
amps through the wires on a hot summer day could overload them.

So... it depends.

Scott

Scott McCalmont, P.E.
McCalmont Engineering
San Jose, CA
(408) 204-0318


On Thu, Mar 4, 2010 at 3:02 PM, Michael Kelly <[email protected]
<mailto:[email protected]>> wrote:

    Kirpal,

    That was always my interpretation as well.  So in the case of a 400A
    service, I can backfeed 400A when utilizing a supply side
    connection.  Others have thoughts on this?
    - Mike

    --
    Michael Kelly
    Project Manager / Project Engineer
    NABCEP Certified Solar PV Installer ™

    SolarFlair Energy, Inc.
    11 Mayhew Street
    Framingham, MA 01702
    Direct Mobile: 617-899-9840
    Main Phone: 508-293-4293
    Main Fax: 508-293-4003
    [email protected] <mailto:[email protected]>


    On Thu, Mar 4, 2010 at 4:16 PM, Kirpal Khalsa <[email protected]
    <mailto:[email protected]>> wrote:

        Mike.....i may be wrong....but I think i am right....you are
        limited by the wire size feeding the supply and/or  the
        transformer size which supplies the service.....depending on the
        physical location of the tap you may be limited by the enclosure
        and the enclosure ratings as well
        would love to hear any other ideas...
        Cheers,
        --
        Sunny Regards,
        Kirpal Khalsa

        NABCEP Certified Solar PV Installer
        Renewable Energy Systems
        www.oregonsolarworks.com <http://www.oregonsolarworks.com/>
        541-218-0201 m
        541-592-3958 o


        On Thu, Mar 4, 2010 at 12:50 PM, Michael Kelly
        <[email protected] <mailto:[email protected]>> wrote:

            Hi All,
            Next to grounding, I find the calculation of the maximum
            amount of backfeed current allowed in a supply side
            connection to be the most vague issue in Article 690.  Let's
            assume we have a 400A, 480/277 service in a commercial
            building, a 400A main service disconnect, and the
            jurisdiction is under NEC 2008.  What is the maximum
            backfeed current allowed in a supply side connection?  The
            only place the code points you to is 230.82(6), which is no
            help, or to Article 705, which is no help either.  I know
            that in the draft version of NEC 2011, there is
            an expansion of 705.12(A) which states "* *Supply Side. An
            electric power production source shall be permitted to be
            connected to the supply side of the service disconnecting
            means as permitted in 230.82(6). The sum of the ratings of
            all overcurrent devices connected to power production
            sources shall not exceed the rating of the service."  That
            is a helpful sentence from the Code, but as it is in draft
            form, what do we do under NEC 2008?  What have you used as a
            maximum backfeed current for supply side connections?
            Thanks,
            Mike
            --
            Michael Kelly
            Project Manager / Project Engineer
            NABCEP Certified Solar PV Installer ™

            SolarFlair Energy, Inc.
            11 Mayhew Street
            Framingham, MA 01702
            Direct Mobile: 617-899-9840
            Main Phone: 508-293-4293
            Main Fax: 508-293-4003
            [email protected] <mailto:[email protected]>

            _______________________________________________
            List sponsored by Home Power magazine

            List Address: [email protected]
            <mailto:[email protected]>

            Options & settings:
            http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

            List-Archive:
            http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

            List rules & etiquette:
            www.re-wrenches.org/etiquette.htm
            <http://www.re-wrenches.org/etiquette.htm>

            Check out participant bios:
            www.members.re-wrenches.org
            <http://www.members.re-wrenches.org/>





        _______________________________________________
        List sponsored by Home Power magazine

        List Address: [email protected]
        <mailto:[email protected]>

        Options & settings:
        http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

        List-Archive:
        http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

        List rules & etiquette:
        www.re-wrenches.org/etiquette.htm
        <http://www.re-wrenches.org/etiquette.htm>

        Check out participant bios:
        www.members.re-wrenches.org <http://www.members.re-wrenches.org/>




    _______________________________________________
    List sponsored by Home Power magazine

    List Address: [email protected]
    <mailto:[email protected]>

    Options & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    List-Archive:
    http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm
    <http://www.re-wrenches.org/etiquette.htm>

    Check out participant bios:
    www.members.re-wrenches.org <http://www.members.re-wrenches.org>





_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options&  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules&  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to