I agree with Warren, the batterys have a big job to do here,   If you have a 48 
volt system the batteries will have to supply about 180 amps, this is a large 
surge and your need to be large or fast the AGM are good for surge, flooded 
would have to be larger (AH) to handle the same surge.  
 
The inverter system could be one of several I have done a similar system on a 
120 amp surge,  I used Outback, and when the big motor was called, I used two 
relays, when the call for pump the first relay closed and energized the extra 
Outbacks, then the second relay wihch was a time delay closed to energize the 
load.  When the load had stabilized the extra outbacks would turn off.  For 
your situation I would recomend two Outbacks,  The master slave, on energy 
save, turn on usually is not fast enough and the surge will kick out the first 
inverter.      
 

 

--- On Thu, 3/18/10, Warren Lauzon <wind...@wind-sun.com> wrote:


From: Warren Lauzon <wind...@wind-sun.com>
Subject: Re: [RE-wrenches] Small Wh and large LRA
To: "RE-wrenches" <re-wrenches@lists.re-wrenches.org>
Date: Thursday, March 18, 2010, 5:41 AM



 _filtered #yiv63337450 {
font-family:Comic Sans MS;}
 _filtered #yiv63337450 {
font-family:ArialMT;}
 _filtered #yiv63337450 {margin:1.0in 1.25in 1.0in 1.25in;}
#yiv63337450 P.MsoNormal {
MARGIN:0in 0in 0pt;FONT-FAMILY:"Times New Roman";FONT-SIZE:12pt;}
#yiv63337450 LI.MsoNormal {
MARGIN:0in 0in 0pt;FONT-FAMILY:"Times New Roman";FONT-SIZE:12pt;}
#yiv63337450 DIV.MsoNormal {
MARGIN:0in 0in 0pt;FONT-FAMILY:"Times New Roman";FONT-SIZE:12pt;}
#yiv63337450 A:link {
COLOR:blue;TEXT-DECORATION:underline;}
#yiv63337450 SPAN.MsoHyperlink {
COLOR:blue;TEXT-DECORATION:underline;}
#yiv63337450 A:visited {
COLOR:blue;TEXT-DECORATION:underline;}
#yiv63337450 SPAN.MsoHyperlinkFollowed {
COLOR:blue;TEXT-DECORATION:underline;}
#yiv63337450 P.MsoAutoSig {
MARGIN:0in 0in 0pt;FONT-FAMILY:"Times New Roman";FONT-SIZE:12pt;}
#yiv63337450 LI.MsoAutoSig {
MARGIN:0in 0in 0pt;FONT-FAMILY:"Times New Roman";FONT-SIZE:12pt;}
#yiv63337450 DIV.MsoAutoSig {
MARGIN:0in 0in 0pt;FONT-FAMILY:"Times New Roman";FONT-SIZE:12pt;}
#yiv63337450 P {
FONT-FAMILY:"Times New Roman";MARGIN-LEFT:0in;FONT-SIZE:12pt;MARGIN-RIGHT:0in;}
#yiv63337450 SPAN.EmailStyle18 {
FONT-FAMILY:Arial;COLOR:navy;}
#yiv63337450 DIV.Section1 {
}


The kicker is the large startup, so you may need to use batteries with low 
internal resistance, such as the Concorde AGM's. You will also have to make 
sure your cables are good for the max current to avoid any voltage drop which 
would cause a low voltage shutdown.
 
Aside from that, just go with around 200-250 AH of battery storage (assuming 12 
volts). A pair of golf car size batteries would probably work if they are 
something like Crown or Trojan.
 
..................................................................................................
Northern Arizona Wind & Sun - Electricity From The Sun Since 1979
Solar Discussion Forum: http://www.wind-sun.com/ForumVB/
..................................................................................................

----- Original Message ----- 
From: Mark Dickson 
To: 'RE-wrenches' 
Sent: Wednesday, March 17, 2010 2:56 PM
Subject: [RE-wrenches] Small Wh and large LRA



Hello Wrenches, 
I’ve been asked to design a battery based PV system for a load that has a high 
start up surge of about 62A @ 115V.  The thing is, once it is running it will 
only run for ~10 minutes per day at 11A.  So the daily loads are very low.  How 
do I size a battery bank large enough to handle the large start-up surge, yet 
reasonable enough to cover the modest daily load?  Is there a rule-of-thumb for 
this?
 

Best regards,
 
Mark Dickson,
NABCEP Certified Solar PV Installer ™
Oasis Montana Inc.



_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


-----Inline Attachment Follows-----


_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




      
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org