The kicker is the large startup, so you may need to use batteries with low 
internal resistance, such as the Concorde AGM's. You will also have to make 
sure your cables are good for the max current to avoid any voltage drop which 
would cause a low voltage shutdown.

Aside from that, just go with around 200-250 AH of battery storage (assuming 12 
volts). A pair of golf car size batteries would probably work if they are 
something like Crown or Trojan.

..................................................................................................
Northern Arizona Wind & Sun - Electricity From The Sun Since 1979
Solar Discussion Forum: http://www.wind-sun.com/ForumVB/
..................................................................................................
  ----- Original Message ----- 
  From: Mark Dickson 
  To: 'RE-wrenches' 
  Sent: Wednesday, March 17, 2010 2:56 PM
  Subject: [RE-wrenches] Small Wh and large LRA


  Hello Wrenches, 

  I've been asked to design a battery based PV system for a load that has a 
high start up surge of about 62A @ 115V.  The thing is, once it is running it 
will only run for ~10 minutes per day at 11A.  So the daily loads are very low. 
 How do I size a battery bank large enough to handle the large start-up surge, 
yet reasonable enough to cover the modest daily load?  Is there a rule-of-thumb 
for this?

   

  Best regards,

   

  Mark Dickson,

  NABCEP Certified Solar PV Installer T

  Oasis Montana Inc.



------------------------------------------------------------------------------


  _______________________________________________
  List sponsored by Home Power magazine

  List Address: [email protected]

  Options & settings:
  http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

  List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

  List rules & etiquette:
  www.re-wrenches.org/etiquette.htm

  Check out participant bios:
  www.members.re-wrenches.org

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to