Erika, You should refer to NEC 690.8 this information. There are two issues that contribute to the 1.56 factor. First is that the maximum current from the PV array is considered the short circuit current multiplied by 1.25 to account for higher than standard irradiance such as cloud edge effect, high altitude, and high operating temperature. The second multiplier of 1.25 is because PV current is considered to be continuous. All conductors (and breakers) operating continuously (over three hours I believe) that are subject to NEC rules are limited to 80% of the ampacity in Table 310.16. The two 1.25 factors equals 1.56. For normal operation, wires selected under this criteria are conservatively rated. But it is also the objective of the NEC to design power systems in a manner that they will remain safe under abnormal circumstances. Kent Osterberg Blue Mountain Solar, Inc. Erika M. Weliczko wrote:
|
_______________________________________________ List sponsored by Home Power magazine
List Address: [email protected] Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org