Ray:

It is my analysis that combiner breakers (if present) will protect only wiring upstream of the combiner -- that is, the individual string circuits. This protection would happen if there is a fault in one individual string (in the wiring or the modules) that allows current from other strings, in excess of the breaker rating, to be supplied through the breaker feeding the faulted string.

There are two scenarios at play here:

1. Any fault between the combiner and the feeder destination will not trip any circuit breakers. The breakers are sized such that the current from each individual string is less than the breaker rating (by more than 1.56 times) and they will not open.

2. PV GFDI protection at the destination end of a feeder will not help. PV GFDI circuits will not remove power from a feeder and they will open the ground-to-grounding conductor bond.

Analyzing this further: Fault conditions are made more likely given that PV string circuits are no longer protected by conduit. Faults are then more likely in individual string circuits (those circuits without conduit protection). This is most problematic at installations with two or fewer strings, where there is no combiner, i.e. residential installations. Statistically, residential installations offer greater exposure to electrical fires because: occupancy occurs for more hours per year, fire alarms and sprinklers are often not installed, children are more often present and standards are more lenient for residential wiring systems.

These two facts are PVs dirty little secrets.  Further innovation is needed...

William Miller


At 12:22 PM 4/5/2010, you wrote:
I think the 100% rating exception is an interpretation issue. I consider the assembly to be defined as the breaker mounted in its listed enclosure. I agree that the AFIs would add cost, but they might actually offer some protection too. (possibly one AFI unit could offer protection for multiple circuits?) I've never had a PV circuit breaker actually trip, except some nuisance tripping due to faulty breakers. PV breakers seem to only offer protection for very limited situations ie, a short in a PV wire being backfed by enough other PV circuits to trip the breaker. It could happen, but I've never actually seen it. Even completely shattered modules still have enough internal resistance to limit the short circuit current to
a value below the breaker trip point.

Ray

On Apr 4, 2010, at 11:47 PM, Kent Osterberg wrote:
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to