Thanks very much Steve;

I still have 2 questions: does the temp sensor control all voltage set points  
or just absorption and float voltage?
2) I'm still a little confused about the absorption time, and refloat, rebulk 
features. for instance, what is the difference between refloat and rebulk?

Apparently his system was getting stuck in a mode where it couldn't quite 
satisfy the absorption time, and would cycle back and forth into a refloat 
mode, etc. Is it possible that the temp sensor was causing the sell voltage 
setting to drop below the refloat voltage? or that, as the temp of the battery 
rose through the day, the set points kept changing and never quite get met?

R. Walters
[email protected]
Solar Engineer




On Apr 5, 2010, at 11:02 AM, Steve Higgins wrote:

> Here is a bit more on how RE-BULK and RE-FLOAT interact with the ABSORB 
> timer. All battery voltages are default and are given as 12VDC nominal, 
> multiply by 2 for 24V and 4 for 48V systems. All of the following is true for 
> grid-tie GV or GT FXs only. 
> 
> 
> After the battery voltage reaches the Absorption set point, the absorption 
> timer starts counting down and maintains absorption voltage for the 
> absorption time. Watching the absorption time is the indication of how long 
> the FX will be in the absorption mode. 
> 
> After the absorption mode is finished, the next stage is Sell RE. Sell RE is 
> a target that the FX cannot charge too, but can export renewable energy if 
> the source is powerful enough. Towards the end of the day, typical renewable 
> energy, like solar, is not available so the FX cannot export any more power. 
> In this event the FX will go silent/passthru, which means it stops any power 
> conversion. 
> 
> The battery usually still has small DC loads, so battery voltage may slowly 
> fall during the night. If the battery voltage falls below the RE-FLOAT 
> setpoint (12.5 volts) then the FX will transition to the FLOAT stage and 
> charge the battery to the FLOAT target (13.6 volts) for the FLOAT time (1 
> hour). After the FLOAT timer has expired, the FX returns to the SellRE stage 
> and/or silent/passthru. 
> 
> If the battery falls past the REFLOAT setpoint, below 12.4 volts (which we 
> call RE-BULK), the FX will change to the BULK stage and the absorption time 
> remaining will start counting up. The absorption time remaining will count up 
> in real time as long as the battery voltage is 12.4 volts or below. The 
> absorption time remaining counts in double time if the battery voltage is 
> less than 12.0 volts and counts in quadruple time if battery voltage is less 
> than 11.6 volts. In other words the lower the battery voltage goes the more 
> time the system will have to remain in the absorption stage up to the 
> absorption time setpoint. 
> 

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]