All of us agree our goal is to increase total production and reduce cost of the 
system over its life. Basically : total lifetime KWH production /  total system 
cost. 
If I can increase the production for the dollar spent by using bigger wire, 
I'll do that, and if it makes more power for the money to add a module, I do 
that.
Basically, I think the volt drop issue comes down to the following:
Inverter to grid not more than 1.5% drop.
Not more than 5% total losses ( code suggested, but not required)
So that leaves up to 3.5% losses from the array to inverter.
anything under 1% begins to get really expensive, so I'm playing in about  +/- 
1 either side of 2% for best economics.
Its all about designing the most system for the money: I do this same cost 
benefit math for framing and layout, tracking, module choice, MPPT, inverter 
choice, wire choice, etc. 
Surprised everyone's getting so concerned over a few watts on the line, when 
module, inverter, and layout choices will have a much larger effect on long 
term production.
(ie. I spend the money saved on wire to buy better monocrystalline)
 
Ray

Friends don't let friends buy amorphous......


On Apr 7, 2010, at 5:09 PM, Joel Davidson wrote:

> Hello Ray,
> I agree with Bob-O. Smaller wires between the inverter and the grid may meet 
> ampacity requirements and your I2R design goal, but high grid-tie voltage has 
> been a problem. Also, 1% of lost power over the life of a PV system adds up 
> especially when grid power continues to go up in price. I agree your 
> reasoning, but I also agree with Feed-In Tariff PV system operators who want 
> every kWh possible and are willing to pay the up-front cost. I'm sticking 
> with less than less than 1% wire loss between the inverter and the grid and 
> less than 2% overall wire loss unless the customer explicitly states that he 
> wants more loss.
> Joel Davidson
> 
> ----- Original Message ----- From: "Bob-O Schultze" 
> <[email protected]>
> To: "RE-wrenches" <[email protected]>
> Sent: Wednesday, April 07, 2010 1:50 PM
> Subject: Re: [RE-wrenches] DC wire sizing
> 
> 
>> Ray,
>> Sorry, I'm not buying that argument over a 25+ year design lifespan. Also, 
>> -and perhaps something many folks don't consider- the NEC requires a MAX 
>> loss of ≤5% over the ENTIRE circuit. That means all the way to the mains 
>> panel. Best practices would require no more than 1.5% VD between the 
>> inverter and the mains so as to avoid any potential of overvoltage 
>> disconnection by the inverter. As it tries to push the current into the 
>> grid, it also pushes up the voltage on that line and on it's own sensors. 
>> Obviously, the larger the current flow and the higher the VD, the worse the 
>> situation could be. Bear in mind that the grid is not held to the same over 
>> and under voltage specifications as your inverter is. 3% + 1.5% is pushing 
>> it just a bit too close for comfort and I still think wasting watts in wire 
>> losses is bad design. We agree that orienting PVs to an azimuth other than 
>> 180° and a bit less than latitude elevation is less than ideal, but you "run 
>> what you brung" in terms of the orientation and roof pitch of a structure. 
>> Better to take a hit on production if we're talking about the backasswards 
>> method of incentivizing by the installed watt, than not installing PV at 
>> all. That said, we DO have control over wire sizing. IMO, throwing away 
>> watts forever just to cheapen it up a very little bit upfront is poor 
>> economy and as the price of gird supplied power increases over the years, 
>> the waste and lost revenue is even more acerbated.
>> Best, Bob-O
>> 
>> On Apr 6, 2010, at 6:04 PM, R Ray Walters wrote:
>> 
>> Just run the numbers sometime. Compare the cost difference of #6 vs. #4 wire 
>> say, and then look at how many more watts you're actually saving, then 
>> multiply that additional wattage by the installed cost per watt.
>> Very simply, once you've satisfied code requirements, there is a point at 
>> which it is cheaper to add more panels than use bigger wire.
>> Also, that point is a moving target that fluctuates with PV and wire costs. 
>> I've found recently for our projects, that that point is falling at about 3% 
>> loss.
>> I also include a cost factor for oversizing the conduit, extra labor (bigger 
>> wire is harder to handle), and any connectors needed to land the larger wire.
>> I've got very well designed systems working for decades, using this method.
>> This is how large commercial systems are designed as well.
>> You can't simply pull 1%, and then call us bad designers because we actually 
>> do an economic analysis for each wire run.
>> It used to be unheard of to install PV facing anything but due south at 
>> latitude tilt, but now we know to add a few more modules. Same concept.
>> 
>> R. Walters
>> [email protected]
>> Solar Engineer
>> 
>> 
>> 
>> 
>> On Apr 6, 2010, at 1:37 PM, Bob-O Schultze wrote:
>> 
>>> Ray,
>>> A 2% wire loss is the generally accepted metric for battery based systems 
>>> with relatively low PV voltage input (<150Voc). It's just plain bad design 
>>> to accept more than a 1% VD on higher voltage systems. PVs ain't THAT cheap.
>>> Best, Bob-O
>>> 
>>> On Apr 6, 2010, at 11:44 AM, R Ray Walters wrote:
>>> 
>>> 
>>> Once I have fulfilled NEC min. requirements, I use a spreadsheet to analyze 
>>> the cost of larger wire vs. the cost of power lost. Going under 2% is 
>>> usually not worth it, if copper prices are high, and PV cost is low enough 
>>> (current market). Sizing for under 2% was good economics a few years back, 
>>> when PV was high, and copper was low, though.
>>> 
>>> For NEC 2011, I agree: while I readily welcome development of DC AFI, 
>>> implementing code before the technology is ready, is a bad idea. But that 
>>> may be the only way to get the technology in place.....
>>> 
>>> Ray
>>> 
>>> On Apr 6, 2010, at 11:15 AM, Kent Osterberg wrote:
>>> 
>>>> Ray,
>>>> 
>>>> Considering that we design PV wiring to be efficient with voltage (and 
>>>> power) loss typically less than 2%, the wire size is nearly irrelevant to 
>>>> arcing issues.   Essentially all the energy available from the PV array 
>>>> can be dissipated in the dc arc.   And since the current is limited by the 
>>>> nature of the IV curve, breakers alone usually won't clear the fault.  The 
>>>> best combiner breakers can do (if you have enough parallel circuits) is 
>>>> isolate the fault to one string in the PV array. With one string being 1 
>>>> or 2 kW in many systems there is still the potential for a lot of heat.
>>>> 
>>>> With the 2011 code just around the corner and no dc arc fault protection 
>>>> on the horizon, it looks like our industry is again going to have a code 
>>>> requirement that no one can fulfill.
>>>> 
>>>> Kent Osterberg
>>>> Blue Mountain Solar, Inc.
>>> 
>>> _______________________________________________
>>> List sponsored by Home Power magazine
>>> 
>>> List Address: [email protected]
>>> 
>>> Options & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>> 
>>> List-Archive: 
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>> 
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>> 
>>> Check out participant bios:
>>> www.members.re-wrenches.org
>>> 
>>> 
>> 
>> _______________________________________________
>> List sponsored by Home Power magazine
>> 
>> List Address: [email protected]
>> 
>> Options & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> List-Archive: 
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> 
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> 
>> Check out participant bios:
>> www.members.re-wrenches.org
>> 
>> 
>> 
>> _______________________________________________
>> List sponsored by Home Power magazine
>> 
>> List Address: [email protected]
>> 
>> Options & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> List-Archive: 
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> 
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> 
>> Check out participant bios:
>> www.members.re-wrenches.org
>> 
> 
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: [email protected]
> 
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to