Allan -

What is the application? Are you trying to switch a large PV array before the 
inverter but after the strings have been fused and combined?

-August

August Goers


Luminalt Energy Corporation
O: 415.564.7652
M: 415.559.1525
F: 650.244.9167
www.luminalt.com<http://www.luminalt.com/>

________________________________
From: [email protected] 
[[email protected]] On Behalf Of Allan Sindelar 
[[email protected]]
Sent: Monday, April 12, 2010 12:41 PM
To: RE-wrenches
Subject: [RE-wrenches] 600VDC Safety Switch question

Wrenches,
We need recommendation of a 200A or larger (400A or 600A preferred) two-pole or 
three-pole, double-throw, 600VDC rated, manually operated, load-break- and 
load-make-rated, service-equipment rated, fusible or nonfusible safety switch 
for purposes of switching DC input.

Square D 82345R and H82345 are rated only 250VDC in a fine-print note in their 
catalog.

I don't think that what I'm asking for exists, but wiser Wrenches may prevail. 
Can anyone suggest another brand and product model that meets these 
requirements?

Thank you,
Allan
--
Allan Sindelar
[email protected]<mailto:[email protected]>
NABCEP Certified Photovoltaic Installer
EE98J Journeyman Electrician
Positive Energy, Inc.
3201 Calle Marie
Santa Fe, New Mexico 87507
505 424-1112
www.positiveenergysolar.com<http://www.positiveenergysolar.com/>
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to