Wrenches,

Please note that Enphase has completed testing and received listing for the ac connectors and the DC connectors for use as the disconnect as required by the NEC.  No other disconnect device is required.  This information is contained in the latest Installation and Operations manual, available for download from http://www.enphaseenergy.com/support/downloads.cfm

See ya!

Marv
707 763-4784  x7016


Dana Orzel wrote:

This is per our AHJ.

 

Thanks,

 

Dana Orzel

Great Solar works, Inc.

E - [email protected]

V - 970.626.5253

F - 970.626.414

C - 970.209.4076

 

From: [email protected] [mailto:[email protected]] On Behalf Of benn kilburn
Sent: Wednesday, May 19, 2010 3:21 PM
To: Wrenches
Subject: Re: [RE-wrenches] Enphase System Labeling

 

Thanks for sharing that Dana,

 

Are you required by code or the AHJ, for micro-inverter systems, to have an additional AC d/c aside from the branch circuit breaker? (on the roof or other location)

 

For these micro-inverter systems the only labeling required here, by code (CEC), is;

84-030 (1) which states...   

“ A warning notice of an interconnected system shall be installed in a conspicuous place at the supply authority disconnecting means of Rule 84-022 and the supply authority meter location.”

 

84-022 is generally referring to the load center main breaker.  And the utility company puts their own "WARNING: interconnected system" label at the meter.

 

So we don't 'have to' provide any additional info, but i think that providing some is a good idea. As Ray pointed out, too much info can be discouraging.

 

For now, I have opted for these labels on the load center as the only labeling for the system;

Code required -- "WARNING Two Power Source Parallel System" and;

Optional for info -- "Grid-Connected Solar Electric System

                                    Array Rating: 660 WDC

                                Module Rating (each): 220 WDC"

....the optional one will of course need to be replaced and updated if/when the owner decides to add to his system.

 

cheers,

benn


DayStar Renewable Energy Inc. 

780-906-7807 

HAVE A SUNNY DAY

 

 


From: [email protected]
To: [email protected]
Date: Mon, 17 May 2010 14:29:12 -0600
Subject: [RE-wrenches] Enphase System Labeling

This was our last batch

 

 

 

          Labeling For Grid-tie Solar Electric System

Great Solar Works, Inc., 970-626-5253

 

                                                                KNOPP SIGNS      

 

Qty – 2, Color red

 

INTERACTIVE SYSTEM POINT OF INTERCONNECTION

Enphase Micro-Inverters [1] per module [17] Total

 

PHOTOVOLTAIC SYSTEM SOURCE

 

                  PV System Total Watts                                            3.910   KW

                  Maximum AC Output Operating Current             13.6     Amps

                  AC Operating Voltage                                              240      Volts 

                 

For information and service contact:

Great Solar Works, Inc., 970-626-5253

 

Qty – 1, Color red

 

PHOTOVOLTAIC SYSTEM SOURCE

 

                  PV System Total Watts                                            3.910   KW

                  Maximum AC Output Operating Current             13.6     Amps

                  AC Operating Voltage                                              240      Volts 

                 

For information and service contact:

Great Solar Works, Inc., 970-626-5253

 

Qty – 1, Color red

 

PHOTOVOLTAIC AC SYSTEM UTILITY DISCONNECT

WARNING - ELECTRIC SHOCK HAZARD - DONOT TOUCH TERMINALS.

TERMINALS ON BOTH THE LINE AND LOAD SIDES MAY BE ENERGIZED

IN THE OPEN POSITION. IF A GROUND FAULT IS INDICATED THE NORMALLY GROUNDED CONDUCTORS MAY BE ENERGIZED AND UNGROUNDED

 

For information and service contact:

Great Solar Works, Inc., 970-626-5253

 

Qty -1, Color Yellow

 

PHOTOVOLTAIC SYSTEM CONNECTED

THE AC PV DISCONNECT IS LOCATED

Next to Meter on South Wall

For information and service contact:

Great Solar Works, Inc., 970-626-5253

 

 

 

Thanks,  Dana Orzel

 

Great Solar Works, Inc

E - [email protected]

V - 970.626.5253

F - 970.626.4140

C - 970.209.4076

web - www.solarwork.com

Responsible Technologies for Responsible People since 1988"

 

 


30 days of prizes: Hotmail makes your day easier! Enter now


_______________________________________________ List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

  
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to