Hello Daryyl,

California electric utilities base their monthly demand charge on the highest 15 consecutive minutes kW demand for each month. PV clients can have excellent mid-day demand reduction until 15 minutes and 1 second of clouds occurs. Then that high demand sets the monthly rate. However, demand management with or without PV can significantly reduce the monthly demand charge.

For more information see http://www.sce.com/NR/rdonlyres/DE3375D0-8402-43CC-ABE1-38C65682B6CF/0/527V10707TOUPAB.pdf

and http://communities.nrri.org/c/document_library/get_file?p_l_id=49730&folderId=49865&name=DLFE-2208.pdf

Joel Davidson


----- Original Message ----- From: "Peter Parrish" <[email protected]>
To: "'RE-wrenches'" <[email protected]>
Sent: Saturday, June 26, 2010 1:25 PM
Subject: Re: [RE-wrenches] Demand savings from PV FYI


Darryl,

I'm sure what you say is generally true, but unless your utility has an
enlightened tariff, I still think we have a problem.

Since the demand charges are based on the highest demand recorded on a
trailing 12 month basis, what happens on that one sunny hot day when a cloud
passes in front of the sun for 15 minutes and the recorded demand for that
time period is recorded and the demand then snaps back to historical values.

In SCE territory, I believe, the demand charge gets pegged at that value for
the next 12 months, regardless.

Please explain to me anything I'm missing.

- Peter


Peter T. Parrish, Ph.D., President
California Solar Engineering, Inc.
820 Cynthia Ave., Los Angeles, CA 90065
CA Lic. 854779, NABCEP Cert. 031806-26
[email protected]
Ph 323-258-8883, Mobile 323-839-6108, Fax 323-258-8885



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Darryl
Thayer
Sent: Saturday, June 26, 2010 7:21 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Demand savings from PV FYI

Hi all
A while back we had a thread going on demand savings from PV.  I reciently
viewed a 1 year data set.  The PV Savings were $36/ month on energy and
almost $100 a month on Demand. The company is a small business with lots of computers and of course air conditioning We are blessed with a diurnal temp
swing.  so morning are cool, and economizers are effective.  The builoding
does not have building automation system.

The summer demand is by far the highest, Every monthly peak occured in the
afternoon, The highest peaks were on sunny days in the afternoon, the solar
reduced all the highest demand peaks.  The Demand fee structure is both a
monthly charge and a ratchet that follows the highest peak for 11 months.
The system is 12 Outback inverters.

BTW the smud program with Silent Power should reduce both utility and
customer demand charges.


_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to