Hi Mick, Take a look at NEC250.32 TerryQuoting Mick Abraham <[email protected]>:

Greetings, Wrenches~ I'm advising some clients on an existing off grid power
system. They have inverters and multiple AC sub-panels which feed several
different structures. The various structures have their own breaker panels.
The power runs 50 feet here, 20 feet there, 60 feet this-a-way and 220 feet
that-a-way. In this African location there are no code inspectors; just a
wish to do things right.

The gentleman who does their wiring installation has written as follows: "I
am not sure whether it is right or not, but I have bonded netural to the
ground rod at each box.  The electrical container is grounded with 4 rods
and all the grounds (at all sub-panels and main panels are all tided
together. I tried to ground everything, everywhere--rods are cheep
insurance."

Mick says: I need to explain as simply as I can how to clean this up.
Normally I would say that the neutral is bonded to earth at only one place
on the entire property...the first AC box after the inverter stack. However,
with one of the sub-panels 220 feet away, does that "single point" advice
still apply? I became confused on this point when an inspector told me that
it was OK to bond the neutral again if the sub-panel was over a certain
distance away...but I can't recall what that distance is and I don't know if
that's in the code or if it's just the opinion of that inspector.

Mick continues: I've heard the term "separately derived" in this context,
but what determines that? If a premise wiring system has a direct electrical
connection to another system, can it even meet the definition of "separately
derived"?

Mick continues: If the client modifies things and reverts to a neutral that
is grounded only at the first disconnect, the next issue is the question of
how the grounds are "tied together". If that bonding occurs by virtue of the
metal lugs on the metal housings of the various metal boxes, we want no
other conductor connecting ground rod A to ground rod B, etc. Is that
correct?

Thanks for helping with my education so I can help with that of my clients.

Mick Abraham, Proprietor
www.abrahamsolar.com

Voice: 970-731-4675




--
Terry

Terry Wessel
President
American Sun Electric/Wessel Electric
PO Box 513
224 Pleasant St.
Blue Hill, ME 04614
Tel: 207.374.5263
Fax: 207.374.3758
http://www.americansunelectric.com


_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to