Bill, Specifically, the additional fusing and disconnect requirement you mentions. Is that each positive and negative PV Source and Output Circuit must have OCPD and go through switched? Twice the combiner boxes, fuses and switches?
Thanks, Ryan J. LeBlanc NABCEPT Certified Solar PV Installer Cell: 707.591.1950 Direct: 707.536.9839 [email protected] http://www.NaturalEnergyWorks.com Ungrounding the array requires additional fusing and disconnects, but the most significant difference is that the module wiring and all external cable must be PV Wire/Cable. Therefore only modules with PV Wire/Cable can be used in these systems. You must confirm from the manufacturer that they have made the switch. Hopefully all manufacturers will be installing PV Wire/Cable soon so that this will not be a problem anymore. _______________________________________________ List sponsored by Home Power magazine List Address: [email protected] Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org