Todd
I've heard the same arguement, as well as its inverse. The battery choice was 
the decision of the system owner. I know they are more sensitive to 
charge/discharge abuse but I see the full charge rate last week at 52.xx V, 
just like day 1and I trust the Trimetric and the Sunny Islands. We're taking 
down the entire system to upgrade & install a 400A transfer switch so the 
batteries will have time to stabilize for the VOC check & cleaning. 
I guess a more accurate question would be is it good enough to properly check 
cell VOC and not bother with the discharge capacity check? A compromise could 
be cap check 12V blocks of cells instead of all 24 separately. Or is the 
capacity checker a waste of money.
Jim
 


 ----Original Message-----
From: [email protected] 
[mailto:[email protected]]on Behalf Of 
[email protected]
Sent: Monday, October 04, 2010 2:23 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Battery capacity testers


  I know many on this list disagree, but this sounds SO typical for sealed 
batteries. It is why I never use em... never! If they are 5 years old, you are 
probably at the limit of their life. Replace em with flooded lead calciums and 
your customers (and you) will be happy for 20+ years.

  my .o2

  Todd



  On Sunday, October 3, 2010 9:28pm, "North Texas Renewable Energy Inc" 
<[email protected]> said:


  I have a customer with a set of 24 Concord PVX-6480s that have twice failed 
during grid outages during the night. No large loads are on the critical load 
panel and, since it's at night when they drop to 50% dod, I'm not sure what's 
up with them. I plan on cleaning and retightning all the cable connections 
first to eliminate that possibility then checking VOC of each cell. 
  Eventually we'll install a 25 kW genset but my first task is to find out the 
state of the batterys. The system turns five next spring so I don't think they 
are near an early death. The BOS is 2 Sunny Island 4248s with upgraded chipsets 
and the charger is set to spec though that may need to be bumped up. The only 
culprit I suspect is the high summer temperatures in this unconditioned 
equipment room. 
  Finally it may be time to invest in a capacity tester. What brand is popular 
among those Wrenches with lots of experience in diagnosing a batterys health? 
The Concord DC5000 only comes in 12 & 24 V models and these are 2V cells. 
  Thanks as always

  Jim Duncan
  North Texas Renewable Energy
  486 W.N. Woody Road
  Azle Texas 76020
  NABCEP Certified Solar PV
  Installer No.31310-57
  TECL 27398
  [email protected] 
  817.917.0527
  www.ntrei.com




  Sent from Finest Planet WebMail.
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to