I was hesitant to reply because I surely will look foolish, but perhaps it may 
help someone in the future. I did something very stupid back in 2001 that 
caused an explosion. 

The battery bank (12 volt, 660AH) was located in a metal cargo container next 
to the wall and set in a plastic container. The container had open doors on 
both ends. The battery was in the absorption cycle with heavy gassing. I 
noticed that the positive terminal was slightly loose. Fully aware of the 
danger of the task I was performing, I grabbed my socket wrench and began to 
carefully snug it down. Even though I carefully observed the location of the 
wrench, I did not think about the steel container wall as having a path back to 
battery negative. It did. I blew the top off a battery that I was standing 
over. Fortunately I was wearing safety glasses or I probably would not be here 
today typing this. There was a water hydrant near and I was able to flood my 
face and body for about 15 minutes. No facial scares but a lessen very well 
learned: Do NOT work on batteries that are off gassing. Gassing begins at about 
2.3 volts per cell. If you are a battery novice, I encourage you to thoroughly 
educate yourself and do not neglect your safety gear when working on batteries.

Another event I witnessed: In 2007 I was at a campground and heard an 
explosion. The owner of an RV a few spaces down from me was opening the battery 
compartment as I walked up. Inside he had  un-vented batteries in the same 
compartment as the inverter and other switch gear. His batteries were obviously 
gassing when something sparked it off. The top was blown off a 6 volt battery 
and he had electrolyte everywhere and a damaged cargo door. We work on hundreds 
of RV's and sadly I see this kind of poor "workmanship" every week at our 
service center.

Larry Crutcher
Starlight Solar Power Systems
928-342-9103
  ----- Original Message ----- 
  From: Kent Osterberg 
  To: RE-wrenches 
  Sent: Wednesday, December 15, 2010 10:21 AM
  Subject: Re: [RE-wrenches] Battery based hydrogen incidents


  Sounds like, in general, that the off-grid industry has been fortunate to not 
have hydrogen explosions.  That's good.  No explosions here either.  But one 
shouldn't take that as evidence that it couldn't happen.  I don't believe this 
is a circumstance where it is better to be lucky than good.  That's why I 
recommend doing the calculations.

  Kent Osterberg
  Blue Mountain Solar



  Dana wrote: 
    Ken - 



    To meet the flow have run 2 and 3 fans to meet the flow. 2" output from the 
fan into a 4" header with a matching 2.5" inlet as far away on the lowest 
portion of the battery box.





    In 22+ years in off grid installations I have yet to see or even hear of 
one hydrogen explosion. I get repeatedly asked why we have to go to the efforts 
we go to for box and venting. I am not able to provide even one incident that I 
have heard rumor of.



    Q - How many battery based hydrogen incidents have happened in our 
collective experience?







    Dana Orzel

    Great Solar Works, Inc

    E - [email protected]

    V - 970.626.5253

    F - 970.626.4140

    C - 970.209.4076

    web - www.solarwork.com



    "Responsible Technologies for Responsible People since 1988"

    Do not ever belive anything, but seriously trust through action.



    From: [email protected] 
[mailto:[email protected]] On Behalf Of Kent Osterberg
    Sent: Tuesday, December 14, 2010 12:07 PM
    To: Wrenches
    Subject: [RE-wrenches] Battery Venting



    Fellow Wrenches,

    The discussion about battery venting reminds me of a useful and inexpensive 
program, BattMV, for determining ventilation requirements per EN-50272.  
EN-50272 is a European standard used to determine how much air flow is needed 
for a room, I don't know of a equivalent standard used in the U.S.  It takes a 
surprising amount of ventilation.  For a 400-AH 48-volt L16 bank charged at 
57.6 volts and 24 amps, it's about 7 CFM just to keep the %H2 down to 4%.  A 
12-volt Zephyr vent is good for about 5 CFM!   If you think you are venting 
enough, take some time and study this issue.

    Kent Osterberg
    Blue Mountain Solar

----------------------------------------------------------------------------
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

  

------------------------------------------------------------------------------


  _______________________________________________
  List sponsored by Home Power magazine

  List Address: [email protected]

  Options & settings:
  http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

  List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

  List rules & etiquette:
  www.re-wrenches.org/etiquette.htm

  Check out participant bios:
  www.members.re-wrenches.org

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to