Some really good lessons here, thanks Larry 
 
I forgot to mention one of my explosions, I was checking connections and found 
one loose but I had turned off the battery bank.  but there were four parallel 
strings connected I believe the string I was working on had a small current 
flowing or some thing because moving the cable to test connection caused 
expolision.  

Inside the battery is hydrogne and oxygen in the perfect ratio, it detonates, 
with almost any spark,  I am sure the flame kernel is much smaller than 
gasoline in air for example.  
Darryl
--- On Wed, 12/15/10, Starlight Solar, Larry Crutcher 
<[email protected]> wrote:


From: Starlight Solar, Larry Crutcher <[email protected]>
Subject: Re: [RE-wrenches] Battery based hydrogen incidents
To: "RE-wrenches" <[email protected]>
Date: Wednesday, December 15, 2010, 1:35 PM



I was hesitant to reply because I surely will look foolish, but perhaps it may 
help someone in the future. I did something very stupid back in 2001 that 
caused an explosion. 
 
The battery bank (12 volt, 660AH) was located in a metal cargo container next 
to the wall and set in a plastic container. The container had open doors on 
both ends. The battery was in the absorption cycle with heavy gassing. I 
noticed that the positive terminal was slightly loose. Fully aware of the 
danger of the task I was performing, I grabbed my socket wrench and began to 
carefully snug it down. Even though I carefully observed the location of the 
wrench, I did not think about the steel container wall as having a path back to 
battery negative. It did. I blew the top off a battery that I was standing 
over. Fortunately I was wearing safety glasses or I probably would not be here 
today typing this. There was a water hydrant near and I was able to flood my 
face and body for about 15 minutes. No facial scares but a lessen very well 
learned: Do NOT work on batteries that are off gassing. Gassing begins at about 
2.3 volts per cell. If you are a
 battery novice, I encourage you to thoroughly educate yourself and do not 
neglect your safety gear when working on batteries.
 
Another event I witnessed: In 2007 I was at a campground and heard an 
explosion. The owner of an RV a few spaces down from me was opening the battery 
compartment as I walked up. Inside he had  un-vented batteries in the same 
compartment as the inverter and other switch gear. His batteries were obviously 
gassing when something sparked it off. The top was blown off a 6 volt battery 
and he had electrolyte everywhere and a damaged cargo door. We work on hundreds 
of RV's and sadly I see this kind of poor "workmanship" every week at our 
service center.
 
Larry Crutcher
Starlight Solar Power Systems
928-342-9103

----- Original Message ----- 
From: Kent Osterberg 
To: RE-wrenches 
Sent: Wednesday, December 15, 2010 10:21 AM
Subject: Re: [RE-wrenches] Battery based hydrogen incidents

Sounds like, in general, that the off-grid industry has been fortunate to not 
have hydrogen explosions.  That's good.  No explosions here either.  But one 
shouldn't take that as evidence that it couldn't happen.  I don't believe this 
is a circumstance where it is better to be lucky than good.  That's why I 
recommend doing the calculations.

Kent Osterberg
Blue Mountain Solar



Dana wrote: 

 _filtered #yiv774257597 {
font-family:Calibri;}
 _filtered #yiv774257597 {
font-family:Tahoma;}
 _filtered #yiv774257597 {
font-family:Century Gothic;}
 _filtered #yiv774257597 {margin:1.0in 1.0in 1.0in 1.0in;}
#yiv774257597 P.yiv774257597MsoNormal {
FONT-SIZE:12pt;MARGIN:0in 0in 0pt;COLOR:black;FONT-FAMILY:"serif";}
#yiv774257597 LI.yiv774257597MsoNormal {
FONT-SIZE:12pt;MARGIN:0in 0in 0pt;COLOR:black;FONT-FAMILY:"serif";}
#yiv774257597 DIV.yiv774257597MsoNormal {
FONT-SIZE:12pt;MARGIN:0in 0in 0pt;COLOR:black;FONT-FAMILY:"serif";}
#yiv774257597 A:link {
COLOR:blue;TEXT-DECORATION:underline;}
#yiv774257597 SPAN.yiv774257597MsoHyperlink {
COLOR:blue;TEXT-DECORATION:underline;}
#yiv774257597 A:visited {
COLOR:purple;TEXT-DECORATION:underline;}
#yiv774257597 SPAN.yiv774257597MsoHyperlinkFollowed {
COLOR:purple;TEXT-DECORATION:underline;}
#yiv774257597 SPAN.yiv774257597EmailStyle17 {
FONT-WEIGHT:normal;COLOR:windowtext;FONT-STYLE:normal;FONT-FAMILY:"sans-serif";TEXT-DECORATION:none;}
#yiv774257597 .yiv774257597MsoChpDefault {
FONT-SIZE:10pt;}
#yiv774257597 DIV.yiv774257597WordSection1 {
}



Ken – 

To meet the flow have run 2 and 3 fans to meet the flow. 2” output from the fan 
into a 4” header with a matching 2.5” inlet as far away on the lowest portion 
of the battery box.


In 22+ years in off grid installations I have yet to see or even hear of one 
hydrogen explosion. I get repeatedly asked why we have to go to the efforts we 
go to for box and venting. I am not able to provide even one incident that I 
have heard rumor of.

Q - How many battery based hydrogen incidents have happened in our collective 
experience?




Dana Orzel
Great Solar Works, Inc
E - [email protected]
V - 970.626.5253
F - 970.626.4140
C - 970.209.4076
web - www.solarwork.com

"Responsible Technologies for Responsible People since 1988"
Do not ever belive anything, but seriously trust through action.



From: [email protected] 
[mailto:[email protected]] On Behalf Of Kent Osterberg
Sent: Tuesday, December 14, 2010 12:07 PM
To: Wrenches
Subject: [RE-wrenches] Battery Venting

Fellow Wrenches,

The discussion about battery venting reminds me of a useful and inexpensive 
program, BattMV, for determining ventilation requirements per EN-50272.  
EN-50272 is a European standard used to determine how much air flow is needed 
for a room, I don't know of a equivalent standard used in the U.S.  It takes a 
surprising amount of ventilation.  For a 400-AH 48-volt L16 bank charged at 
57.6 volts and 24 amps, it's about 7 CFM just to keep the %H2 down to 4%.  A 
12-volt Zephyr vent is good for about 5 CFM!   If you think you are venting 
enough, take some time and study this issue.

Kent Osterberg
Blue Mountain Solar
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

  



_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


-----Inline Attachment Follows-----


_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




      
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to