Mark,

It was a 20-kW generator. I don't remember if it was a 100-amp or 200-amp ATS - it wasn't relevant due to the point of connection. Since the ATS was not service rated, a service-rated disconnect had to proceed it. That was to great advantage: 1) while connecting the PV system to the utility side of the ATS, a service side tap wasn't required. 2) The service disconnect switch had double lugs (not on my sketch) so there weren't multiple conductor taps. While I only showed one, this system actually had two non-essential panels: one for the house and one for the barn.

Kent Osterberg
Blue Mountain Solar



Mark Frye wrote:
Ken,
 
In the situation you show in your drawing, what was the rating of the transfer switch?
 
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City,  CA 95959
(530) 401-8024
www.berkeleysolar.com 
 


From: [email protected] [mailto:[email protected]] On Behalf Of Kent Osterberg
Sent: Sunday, March 27, 2011 11:37 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Generator and Enphase

Larry,

Situations vary so much that this might not be very useful. But here you go. The attached sketch shows how we recently connected a customer that had a backup generator and transfer switch that wasn't service rated. There were nice gutters existing from the original install so accessing points to tap conductors wasn't difficult. We could have connected the inverters to the non-backed upped loads panel instead, but the utility requires an accessible disconnect by the meter so it was more convenient to just get into the gutter.

Kent Osterberg
Blue Mountain Solar 

_______________________________________________ List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

  
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to