This doesn't solve the reliability concern of a contactor but on a webinar I 
heard a rep from Schneider say the XW (with GEN and GRID AC IN's) will not 
backfeed a generator and will do it without a contactor. Is that true?

Larry Liesner
Wirewiz
Westport, CT
Phone: 203-644-2404
Fax: 203-557-0556
[email protected]
www.wire-wiz.com



On Mar 27, 2011, at 3:50 PM, Kent Osterberg wrote:

> Larry,
> 
> Yes, the PV system was straight grid-tie. The back-upped loads were only 
> covered by the generator (no battery-based inverter was involved). The ATS 
> also does the generator startup, so an inverter on the backed-upped loads 
> would require some thinking I haven't done. If the generator startup were 
> changed, my first thought would be to put the battery-based inverter on the 
> generator side of the ATS.
> 
> Kent Osterberg
> Blue Mountain Solar 
> 
> 
> 
> [email protected] wrote:
>> 
>> Kent,
>> 
>> Situations vary but this one line helps a lot, thanks.
>> 
>> So,  "To PV System" would go to the output of a grid tie inverter and "To 
>> Backed Up Loads" would go to the AC IN (transfer switch) of a battery 
>> inverter. 
>> 
>> I have been going to homes with existing 100A gen/utility ATS and wondering 
>> if I could keep it as is and be able to add a grid tie battery backup to it 
>> (using same backup loads). This schematic would work in that situation as 
>> well but wouldn't have the "To Non-Backed UP Loads" tap.
>> 
>> 
>> Larry Liesner
>> Wirewiz
>> Westport, CT
>> Phone: 203-644-2404
>> Fax: 203-557-0556
>> [email protected]
>> www.wire-wiz.com
>> 
>> 
>> 
>> On Mar 27, 2011, at 2:36 PM, Kent Osterberg wrote:
>> 
>>> Larry,
>>> 
>>> Situations vary so much that this might not be very useful. But here you 
>>> go. The attached sketch shows how we recently connected a customer that had 
>>> a backup generator and transfer switch that wasn't service rated. There 
>>> were nice gutters existing from the original install so accessing points to 
>>> tap conductors wasn't difficult. We could have connected the inverters to 
>>> the non-backed upped loads panel instead, but the utility requires an 
>>> accessible disconnect by the meter so it was more convenient to just get 
>>> into the gutter.
>>> 
>>> Kent Osterberg
>>> Blue Mountain Solar
>>> 
>>> 
>>> 
>>> [email protected] wrote:
>>>> 
>>>> Kent, Jason, or anyone else
>>>> 
>>>> Would you a have a simple one-line you could share for wiring the inverter 
>>>> on the utility side of the transfer switch? 
>>>> 
>>>> Thank you.
>>>> 
>>>> Larry Liesner
>>>> Wirewiz
>>>> Westport, CT
>>>> Phone: 203-644-2404
>>>> Fax: 203-557-0556
>>>> [email protected]
>>>> www.wire-wiz.com
>>>> 
>>>> 
>>>> 
>>>> On Mar 26, 2011, at 6:04 PM, Jason Szumlanski wrote:
>>>> 
>>>>> We’ve explored this strategy many times due to all of the whole house and 
>>>>> critical load generators in Florida. We’ve stayed away from the contactor 
>>>>> solution because of the potential for the NC contactor failing to open, 
>>>>> keeping the inverters “online” when transferred to generator power. While 
>>>>> unlikely, this is a possibility that must be considered.
>>>>>  
>>>>> The other issue presented here is that the inverters will shut down every 
>>>>> time the generator exercises.
>>>>>  
>>>>> The only sure-fire way seems to be wiring the inverter on the utility 
>>>>> side of the transfer switch, as Kent said.
>>>>>  
>>>>> Jason Szumlanski
>>>>> Fafco Solar
>>>>>  
>>>>>  
>>>>> From: [email protected] 
>>>>> [mailto:[email protected]] On Behalf Of Kent 
>>>>> Osterberg
>>>>> Sent: Saturday, March 26, 2011 5:56 PM
>>>>> To: RE-wrenches
>>>>> Subject: Re: [RE-wrenches] Generator and Enphase
>>>>>  
>>>>> Mark,
>>>>> 
>>>>> I agree it is best to wire the inverters on the utility side of the 
>>>>> transfer switch. When that isn't easy, a normally closed contactor that 
>>>>> is opened by generator voltage, will isolate the inverters from the 
>>>>> generator and allow automatic return to utility operation when the 
>>>>> generator is off.
>>>>> 
>>>>> Kent Osterberg
>>>>> Blue Mountain Solar
>>>>> 
>>>>> 
>>>>> 
>>>>> Mark Frye wrote:
>>>>> Eric,
>>>>>  
>>>>> I do not have direct experience with this but have been exploring the 
>>>>> issue for a project I am currently doing.
>>>>>  
>>>>> My response will be to take the trouble to interconnect the Enphase 
>>>>> inverters on the line side of the tranfer switch so that the inverters 
>>>>> can never be connected to the generator.
>>>>>  
>>>>> Here are the reasons why:
>>>>>  
>>>>> 1 - Enphase states that any such application is considered an "off-grid" 
>>>>> application which voids their warrenty. As I am installing under the 
>>>>> California CSI program, I am required to provide a 10 year manufacture 
>>>>> equipment warranty so I cannot afford to install the inverters in a 
>>>>> dis-allowed manner.
>>>>>  
>>>>> 2 - Enphase states that the waveform of the generator may be "clean" 
>>>>> enough such that the inverter may attempt to syncornize and connect to it 
>>>>> as if it were the utility. If this were to happen Enphase believes the 
>>>>> inverters will ruin the generator regulator before the generator ruin the 
>>>>> inverter. I don't want to be the one to run the experiment to find out 
>>>>> which would be which.
>>>>>  
>>>>> 3 - I considered a contactor on the output of the inverters, such that 
>>>>> the inverters would isolated by a loss of line voltage, requiring some 
>>>>> form of reset. Ulitmately my customer agreed with me that this was an 
>>>>> undesirable constraint on the operation of an otherwise reliable 
>>>>> grid-tied system and it was not clear that this would satify the warranty 
>>>>> issue.
>>>>>  
>>>>> Mark Frye 
>>>>> Berkeley Solar Electric Systems 
>>>>> 303 Redbud Way 
>>>>> Nevada City,  CA 95959 
>>>>> (530) 401-8024 
>>>>> www.berkeleysolar.com 
>>>>>  
>>>>>  
>>>>> From: [email protected] 
>>>>> [mailto:[email protected]] On Behalf Of Eric 
>>>>> Thomas
>>>>> Sent: Saturday, March 26, 2011 2:09 PM
>>>>> To: [email protected]
>>>>> Subject: [RE-wrenches] Generator and Enphase
>>>>> 
>>>>> I have a customer with a "30A Mechanically Interlocked Breaker" for their 
>>>>> generator feed at the main panel. My question is: If the home power is 
>>>>> transferred from utility to generator power, will the backfed PV see the 
>>>>> generator as grid power and sync up and produce? This is a nice Honda 
>>>>> Generator so the power should be fairly clean. Any experiences are 
>>>>> appreciated.
>>>>> 
>>>>> Take Care,
>>>>> 
>>>>> 
>>>>> Eric Thomas
>>>>> Solar Epiphany LLC
>>>>> (206) 919-3014
>>>>> www.solarepiphany.com
>>>>> 
>>>>>  
>>>>> _______________________________________________
>>>>> List sponsored by Home Power magazine
>>>>> 
>>>>> List Address: [email protected]
>>>>> 
>>>>> Options & settings:
>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>> 
>>>>> List-Archive: 
>>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>> 
>>>>> List rules & etiquette:
>>>>> www.re-wrenches.org/etiquette.htm
>>>>> 
>>>>> Check out participant bios:
>>>>> www.members.re-wrenches.org
>>>>> 
>>>> 
>>>> 
>>>> _______________________________________________
>>>> List sponsored by Home Power magazine
>>>> 
>>>> List Address: [email protected]
>>>> 
>>>> Options & settings:
>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>> 
>>>> List-Archive: 
>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>> 
>>>> List rules & etiquette:
>>>> www.re-wrenches.org/etiquette.htm
>>>> 
>>>> Check out participant bios:
>>>> www.members.re-wrenches.org
>>>> 
>>>>   
>>> <OneLine.JPG>_______________________________________________
>>> List sponsored by Home Power magazine
>>> 
>>> List Address: [email protected]
>>> 
>>> Options & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>> 
>>> List-Archive: 
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>> 
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>> 
>>> Check out participant bios:
>>> www.members.re-wrenches.org
>>> 
>> 
>> 
>> _______________________________________________
>> List sponsored by Home Power magazine
>> 
>> List Address: [email protected]
>> 
>> Options & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> List-Archive: 
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> 
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> 
>> Check out participant bios:
>> www.members.re-wrenches.org
>> 
>>   
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: [email protected]
> 
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to