I think Kent and I agree. For the case where the subpanel is not dedicated a PV sub-panel he is calculating for 2 - 50A breakers and I calculated for 3 - 50A breakers.
Mark Frye Berkeley Solar Electric Systems 303 Redbud Way Nevada City, CA 95959 (530) 401-8024 <http://www.berkeleysolar.com/> www.berkeleysolar.com _____ From: [email protected] [mailto:[email protected]] On Behalf Of Kent Osterberg Sent: Tuesday, March 29, 2011 9:26 PM To: RE-wrenches Subject: Re: [RE-wrenches] sizing a sub-panel used to combine multiple inverter outputs Per 705.12(D) the sub-panel could be any distribution equipment on the premises. So the question becomes: is the sub-panel capable of supplying branch circuits or feeder loads? If yes, then the sum of the breakers (potentially) feeding the bus is 180 amps so a 150-amp rating is required and the inverters would have to feed the opposite end of the bus bars. If no, the code is not clear on the requirement, but obviously the 80-amp breaker in the main panel limits the maximum current flowing through the sub-panel. Kent Osterberg Blue Mountain Solar
_______________________________________________ List sponsored by Home Power magazine List Address: [email protected] Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org