Wouldn't a fault in that conductor between the main and the sub have a 
potential for up to 160A of current? I would think that at noon on a sunny day, 
the inverter system could produce 80A from one direction (albeit really only 
the max amperage outputs of the inverters) and 80A of grid current from the 
main into a partial fault.

Brian Teitelbaum
AEE Solar

From: [email protected] 
[mailto:[email protected]] On Behalf Of Mark Frye
Sent: Wednesday, March 30, 2011 9:49 AM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] sizing a sub-panel used to combine multipleinverter 
outputs

Al,

I would say that yes the meter is a load and this goes to show the relative 
inadequacy of the vocabulary we are using in the discussion. In the example we 
have been using with the 80A breaker, wire and sub panel, you could have up to 
80A of loads installed in the sub and still not create an over current 
condition in any of that equipment.

Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City,  CA 95959
(530) 401-8024
www.berkeleysolar.com<http://www.berkeleysolar.com/>


________________________________
From: [email protected] 
[mailto:[email protected]] On Behalf Of Al Frishman
Sent: Wednesday, March 30, 2011 9:00 AM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] sizing a sub-panel used to combine multipleinverter 
outputs
Is a monitoring system installed in the Load Center to measure the cumulative 
kWh's of the inverter's considered a load?
The type of monitoring device I am talking about has CT's that go around the 
conductors and the Voltage ref is taken by attaching conductors to each phase, 
the Neutral and the ground bar.    The digital Meter has a 3-pole 5A breaker in 
it so the conductors in the load center can be connected to lugs on the bus bar 
directly.

Al Frishman
AeonSolar
(917) 699-6641 - cell
(888) 460-2867
www.aeonsolar.com<http://www.aeonsolar.com/>


From: [email protected] 
[mailto:[email protected]] On Behalf Of Jason Szumlanski
Sent: Wednesday, March 30, 2011 8:18 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] sizing a sub-panel used to combinemultipleinverter 
outputs

Another key is to remember that this discussion also applies to the conductor 
between the main panel and subpanel. In a large PV system, this could result in 
a pretty large wire between the two panels, and a significant cost that is 
often overlooked. In some cases it makes sense to locate the subpanel close to 
the main panel and run multiple sets of smaller wires from the inverters to the 
subpanel.

And because the calculation is based on the first OC protection connected to 
the inverters, adding a main breaker (theoretically 80A in this example) in the 
subpanel doesn't change things. Even though this wire would be theoretically 
protected by an 80A breaker at each end, you can't size the wire for 160A / 1.2 
= 133.3A. You have to size for 180A/1.2 = 150A. (not that it makes much of a 
difference in this example, but it still must be considered)

At least that's how I understand it...

Jason Szumlanski
Fafco Solar


From: [email protected] 
[mailto:[email protected]] On Behalf Of Mark Frye
Sent: Wednesday, March 30, 2011 1:33 AM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] sizing a sub-panel used to combinemultipleinverter 
outputs

Opps!

My bad, I was thinking of a single phase system, not the three phase system 
shown in the article.

For the three phase system Kent is correct in counting 180A of supply per bar.

Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City,  CA 95959
(530) 401-8024
www.berkeleysolar.com<http://www.berkeleysolar.com/>


________________________________
From: [email protected] 
[mailto:[email protected]] On Behalf Of Mark Frye
Sent: Tuesday, March 29, 2011 10:17 PM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] sizing a sub-panel used to combine multipleinverter 
outputs
I think Kent and I agree. For the case where the subpanel is not dedicated a PV 
sub-panel he is calculating for 2 - 50A breakers and I calculated for 3 - 50A 
breakers.

Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City,  CA 95959
(530) 401-8024
www.berkeleysolar.com<http://www.berkeleysolar.com/>


________________________________
From: [email protected] 
[mailto:[email protected]] On Behalf Of Kent Osterberg
Sent: Tuesday, March 29, 2011 9:26 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] sizing a sub-panel used to combine multiple inverter 
outputs
Per 705.12(D) the sub-panel could be any distribution equipment on the 
premises. So the question becomes: is the sub-panel capable of supplying branch 
circuits or feeder loads? If yes, then the sum of the breakers (potentially) 
feeding the bus is 180 amps so a 150-amp rating is required and the inverters 
would have to feed the opposite end of the bus bars. If no, the code is not 
clear on the requirement, but obviously the 80-amp breaker in the main panel 
limits the maximum current flowing through the sub-panel.

Kent Osterberg
Blue Mountain Solar
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to