Kirpal,

Although I can't answer your IO101 question, I can tell you that the SQ Flex operates nicely for us
when used with a pressure tank/ pressure switch. As long as the pump and PV power source are
sized to accommodate the additional vertical lift caused by the tank pressure, all is good.

As for the 2 current carrying conductors, that still fascinates me. When using 240 AC, the 2 phase
wires from the grid are attached to the blue and brown wires from the pump.

When switched over to the array, the DC positive and negative are attached to the same brown and blue
wires but the polarity doesn't matter. It's all taken care of by the electronics in the pump. Takes a while
to get used to that.

And have you seen the documentation that comes with the pump and CU200? I'm embarrassed to include
them in the customer's document package...they're all pictures and no text....sigh....
Roy Butler
NABCEP Certified Solar PV Installer®
NYSERDA eligible PV & wind installer
PA Sunshine Program Approved PV Installer
Four Winds Renewable Energy, LLC
8902 Route 46
Arkport, NY 14807
607-324-9747

www.four-winds-energy.com

Although no trees were killed in the sending of this message, 
a large number of electrons were terribly inconvenienced.

                

On 4/6/2011 4:55 PM, Kirpal Khalsa wrote:
Hi all....so I have a pumping project using a grundfos SQ Flex pump....It will operate on the grid when grid is present and then switch back to solar ready if the grid power should fail.....here is the set up...
5-Sanyo HIT 220's Vmp non temp adjusted is 213VDC
Pump is SQFlex 16 SQF-10 will have CU 200 controller and IO101 AC input box....

System has a pressure tank and pressure switch which will be used instead of float switch as there is no storage tank at or above ground level....
This system is a retrofit project to an existing well pumping system......
Here is my questions:
1. Pump and CU 200 controller are rated for upto 300VDC but IO 101 Controller is only rated for 225VDC.....is that open circuit or max power on the modules....
2. The Grundfos wiring diagrams only show 2 wires and a ground leaving the IO101 going to the CU200.....What is happening when there is 240VAC supplying the system and what happens when it switches back to DC how is the power transmitted on those wires?  What happens to the second leg of the 240VAC generator/grid input?
3. Has anyone done one of these Grundos SQFlex back up water pumping systems connected to a pressure tank and did it operate as expected?
Grundfos does not offer tech support.......that is kind of a bummer....
Thanks for any advice or help....


--
Sunny Regards,
Kirpal Khalsa
NABCEP Certified Solar PV Installer
Renewable Energy Systems
www.oregonsolarworks.com
541-218-0201 m
541-592-3958 o
_______________________________________________ List sponsored by Home Power magazine List Address: [email protected] Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to