Hi Nathan,

The SQ Flex will take AC or DC voltage.
I suspect your issue is with the CU200 which have  a lot of failures.

jay

peltz power
On Apr 6, 2011, at 4:48 PM, Nathan Jones wrote:

> Allan,
> I seem to recall the SQ Flex pumps will run on 90VAC to 240VAC. I had several 
> lengthy talks with the engineers in the KS. City office re. the failure to 
> stop on command situation. While they were helpful with some aspects they 
> completely denied the situation we were experiencing existed or could exist. 
> This despite the fact that I had stood there and witnessed the event 
> happening real time. They wanted me to take a picture of the controller with 
> the pump running and send it to them?????? We finally opted for a pressure 
> switch to actually break the current to the pump as the CU200 stop command 
> was being ignored by the pump. I don't think I know of any of the installs 
> around here actually seeing the 240AC though but I think it was one of the 
> engineers there who I discussed it with.
> Nathan Jones
> Power Source Solar
>  
> 
> From: Allan Sindelar <[email protected]>
> To: Kirpal Khalsa <[email protected]>
> Cc: RE-wrenches <[email protected]>
> Sent: Wed, April 6, 2011 6:28:35 PM
> Subject: Re: [RE-wrenches] Grundfos SQ Flex
> 
> Kirpal,
> I have never tried to feed 240V to an IO101, so I don't know the answer. But 
> as the pump takes a maximum of only 950-1100 watts (approximate here, from 
> memory). The usual reason for adding an IO101 is to allow a portable 
> generator to back up a PV array during cloudy weather or a broken pipe, and 
> the most portable generators are the little 1kW or 2kW inverter-generators, 
> and the supplied AC pigtail is 15A 120V, so that's all I have ever tried. 
> Sorry.
> 
> You may have to look at a unit directly. I seem to recall it contains an 
> Allen-Bradley AC contactor, and you can check the specs on the contactor 
> directly.
> 
> Sat nam.
> Allan
> 
> Allan Sindelar
> [email protected]
> NABCEP Certified Photovoltaic Installer
> NABCEP Certified Technical Sales Professional
> New Mexico EE98J Journeyman Electrician
> Positive Energy, Inc.
> 3201 Calle Marie
> Santa Fe, New Mexico 87507
> 505 424-1112
> www.positiveenergysolar.com
> 
> 
> 
> 
> On 4/6/2011 5:08 PM, Kirpal Khalsa wrote:
>> 
>> Allan.....According to the IO101 literature it is rated at upto 
>> 265VAC......however in all its wiring "drawings" it only shows one hot, one 
>> neutral and a ground!?? I am puzzled.....?
>> Kirpal
>> 
>> On Wed, Apr 6, 2011 at 2:23 PM, Allan Sindelar 
>> <[email protected]> wrote:
>> Kirpal,
>> I believe that the IO101 is only designed to accept 120VAC, not 240. The 
>> supplied AC pigtail is 15A 120V, and it uses a contactor, which would be a 
>> specific voltage only. Unless I'm mistaken, you don't want to supply 220 
>> (240) VAC.
>> 
>> I don't have answers for your other questions.
>> Allan
>> 
>> Allan Sindelar
>> [email protected]
>> NABCEP Certified Photovoltaic Installer
>> NABCEP Certified Technical Sales Professional
>> New Mexico EE98J Journeyman Electrician
>> Positive Energy, Inc.
>> 3201 Calle Marie
>> Santa Fe, New Mexico 87507
>> 505 424-1112
>> www.positiveenergysolar.com
>> 
>> 
>> 
>> 
>> On 4/6/2011 2:55 PM, Kirpal Khalsa wrote:
>>> Hi all....so I have a pumping project using a grundfos SQ Flex pump....It 
>>> will operate on the grid when grid is present and then switch back to solar 
>>> ready if the grid power should fail.....here is the set up...
>>> 5-Sanyo HIT 220's Vmp non temp adjusted is 213VDC
>>> Pump is SQFlex 16 SQF-10 will have CU 200 controller and IO101 AC input 
>>> box....
>>> 
>>> System has a pressure tank and pressure switch which will be used instead 
>>> of float switch as there is no storage tank at or above ground level....
>>> This system is a retrofit project to an existing well pumping system......
>>> Here is my questions:
>>> 1. Pump and CU 200 controller are rated for upto 300VDC but IO 101 
>>> Controller is only rated for 225VDC.....is that open circuit or max power 
>>> on the modules....
>>> 2. The Grundfos wiring diagrams only show 2 wires and a ground leaving the 
>>> IO101 going to the CU200.....What is happening when there is 240VAC 
>>> supplying the system and what happens when it switches back to DC how is 
>>> the power transmitted on those wires?  What happens to the second leg of 
>>> the 240VAC generator/grid input?
>>> 3. Has anyone done one of these Grundos SQFlex back up water pumping 
>>> systems connected to a pressure tank and did it operate as expected?
>>> Grundfos does not offer tech support.......that is kind of a bummer....
>>> Thanks for any advice or help....
>>> 
>>> 
>>> --
>>> Sunny Regards,
>>> Kirpal Khalsa
>>> NABCEP Certified Solar PV Installer
>>> Renewable Energy Systems
>>> www.oregonsolarworks.com
>>> 541-218-0201 m
>>> 541-592-3958 o
>>> 
>>> _______________________________________________
>>> List sponsored by Home Power magazine
>>> 
>>> List Address: [email protected]
>>> 
>>> 
>>> Options & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>> 
>>> List-Archive: 
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>> 
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>> 
>>> Check out participant bios:
>>> www.members.re-wrenches.org
>>> 
>> 
>> _______________________________________________
>> List sponsored by Home Power magazine
>> 
>> List Address: [email protected]
>> 
>> Options & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> List-Archive: 
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> 
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> 
>> Check out participant bios:
>> www.members.re-wrenches.org
>> 
>> 
>> 
>> 
>> 
>> -- 
>> Sunny Regards,
>> Kirpal Khalsa
>> NABCEP Certified Solar PV Installer
>> Renewable Energy Systems
>> www.oregonsolarworks.com
>> 541-218-0201 m
>> 541-592-3958 o
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: [email protected]
> 
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to