Mark,

NEC 230.2(A) specifically allows two services for parallel power production sources. While a feeder from the house is technically not the same as a service, it should be allowed provided that there is a disconnect grouped with the main service disconnect. A discussion with the inspector ahead of time should make this work smoothly.

Kent Osterberg
Blue Mountain Solar


Mark Frye wrote:
Thanks Nick,
 
250 talks about two seperate buildings with one service, and 230 talks about one building with two services.
 
I don't think this particular situation has been contempated by the Code.
 
How big a deal would it be to just bond the two ground electrode systems together and go along my merry way?

Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City,  CA 95959
(530) 401-8024
www.berkeleysolar.com 
 


From: [email protected] [mailto:[email protected]] On Behalf Of Nick Vida
Sent: Monday, April 18, 2011 12:13 AM
To: wrenches
Subject: [RE-wrenches] Two Buildings, Two Services, One Roof

It seems like it should be fine if you run one conduit to your shop inverter, and another to a dc disconnect and underground to the house inverter, but I see you running a bonding wire for the 2 GECs as well for some reason. You should go through the part of 250 about different GEC for separate building, which has some optional installation options, and you could likely use that to justify running the equipment ground back to the house.

_______________________________________________ List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

  
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to