Bob,

I totally understand the concern about multiple strings *if the strings are 
connected across the battery bank* as had always been the tradition in off-grid 
installations.  My own experience with such a bank in my system  showed why 
when I had a single cell get to near meltdown.  I was lucky to find it.  
Maintenance is another reason, such banks are far more difficult to maintain.  
But I think those concerns are ameliorated a great deal with a buss bar 
installation and once I did that I never had another problem and found the 
battery bank much easier to maintain because the strings no longer had to be 
right next to each other.  Heck, it would be possible to put each series string 
in its own box for that matter.  And with the inclusion of string fuses that 
reduces problems even further.  

When living with an off-grid system my biggest concern was system reliability 
and redundancy and the idea of a single string failure was a big worry which is 
why I never would consider it.

Tom



From: boB Gudgel 
Sent: Tuesday, May 31, 2011 8:16 PM
To: RE-wrenches 
Subject: Re: [RE-wrenches] 24 volt Battery Bank comparison



OK, I've been hearing for years now that one battery string is best and maybe 
two but no more should be used.

What is the reason for this fear ???    What is the experience with multiple 
strings in parallel ??

If it is because of current sharing of the strings, that shouldn't be an 
insurmountable problem if the wiring is done right.

If it has to do with the possibility of fire, which Darryl mentioned, seems 
that series string fuses could mitigate the possibility of that issue, if 
because of shorted cells, just like PV combiners.

Or maybe it has to do with the trouble of getting into the middle of a pile of 
batteries ?  Use battery boxes ?

The strings are in parallel and so they all get the same voltage, theoretically 
anyway if the connections are good.

I would think that the more strings, the LESS stress on individual batteries, 
not more.  The current in each battery should be less than it would be I would 
think.

So what is the real experience ?? 

Is a battery balancer the answer ??

Thanks,
boB







  On May 31, 2011, at 8:23 PM, "Wayne Irwin" <[email protected]> wrote:


    I think the verdict is 12 - Rolls 2-YS-31 2430 AH @ 20 HR (one string) and 
one dry spare in storage is the best case scenario!

    Wayne Irwin, EE
    Director of Engineering
    Pure Energy Solar International Inc. 
    State Licensed Solar Contractor
    License # CVC56695 
    [email protected] 
    http://pureenergysolar.com 
    352 377-6527 Office
    352 336-3299 Fax
    352 316-1637 Cell




--------------------------------------------------------------------------------
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




--------------------------------------------------------------------------------

No virus found in this message.
Checked by AVG - www.avg.com
Version: 10.0.1375 / Virus Database: 1511/3672 - Release Date: 05/31/11
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to