Nick,

It does sound like a ground fault, which leaves the question: why doesn't the SB5000 see enough current to trip? Maybe it is something else. I'd disconnect PV+ and PV- and then measure the string voltage. Even with a ground fault it should be within normal range; if not there is something besides a ground fault. Then measure PV+ to ground and PV- to ground. These two numbers should add up to Voc. The ratio PV-/Voc times the number of modules will tell you about how many modules are between the fault and where the array is normally grounded. Caution: normally grounded conductors, in fact all the conductors, may be energized in reference to ground. Use appropriate personal protective gear.

Kent Osterberg
Blue Mountain Solar



Nick Vida wrote:
Hi wrenches.

I had an interesting case today that I have been thinking about since it happened. I dont have all the details because the homeownter had to leave before I was done with the service call, but here is what I do know. SB5000 with 2 strings of 15 modules. String one was 437 vdc, and string 2 was 247vdc. I decided to look for a ground fault, and I turned off the inverter. I measured for ground faults and found no evidence of anything wrong in that regard. As the homeowner was out of time and wanted me to go, I re-landed the wires in the dc disco, and when I replaced the fuses, I noticed a minor arc when one of the fuses was going it. Although I had no time to measure it, I think that there might be a partial short circuit, possibly with one complete string and some panels of the other string, and the remaining panels on the second string. My mind was racing with how I could have measured for a partial short circuit without seeing it as an arch. I can imagine such a thing on a bigger system being a dramatic electrical event.
needless to say, I cant wait to get back there and go through the signal path properly and find out what the electrician did. And of course i realized that replacing the fuses in such a questionable situation was probably not the best idea.
Do any of you have any thoughts on how one would measure for such a thing?

nick vida


_______________________________________________ List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

  
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to