boB:
I'd like to run the inverters in the normal fashion with generator input
(no PV): (I'd thought these were SW inverters but they are PS series).
1. The inverters power 120 only loads (shared neutral on two feeders) so
the inverters need to be stacked.
2. When the batteries get low, the inverters start the generator. The
inverters transfer through from the generator power to the loads and charge
batteries.
Can the PS pair do this with a three phase generator? I am beginning to
think not...
William
At 10:56 AM 7/28/2011, you wrote:
Do you just want to charge batteries and are these regular 120VAC SWs
?? 120/208 ??
If so, you should just be able to connect each SW from neutral to hot. No
stacking necessary.
A regular SW stacking cable won't work for delta connections because that
assumes
the phases are going to be 180 degrees (120/240) and not 120 degrees
as for 208V delta.
There was a 3 phase version of the SWs which required a separate 3-way
cable and
different software in the SW itself.
boB
On Thu, Jul 28, 2011 at 12:23 AM, William Miller
<<mailto:[email protected]>[email protected]> wrote:
Friends:
Is there any way to connect two SW series inverters to two phases of a
three phase generator? It seems to me that one could connect three SW
inverters with the right stacking cable (or am I confusing Outback
inverters with the hub jumper set properly).
Any input is appreciated.
Thanks,
William
William Miller
Miller Solar
Voice :<tel:805-438-5600>805-438-5600
email: <mailto:[email protected]>[email protected]
http://millersolar.com
License No. C-10-773985
_______________________________________________
List sponsored by Home Power magazine
List Address: [email protected]
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
No virus found in this message.
Checked by AVG - www.avg.com
Version: 10.0.1390 / Virus Database: 1518/3793 - Release Date: 07/28/11
William Miller
Miller Solar
Voice :805-438-5600
email: [email protected]
http://millersolar.com
License No. C-10-773985
_______________________________________________
List sponsored by Home Power magazine
List Address: [email protected]
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org