William,
Just a minor note: if I recall, the PS model was the first to eliminate the generator autostart function and auxiliary relays from the unit. It also eliminated the digital display and control panel. It was intended as a low-cost "base model" of the SW series (I heard some installers that the initials stood for Pile of ...). So I don't think that these units can start the generator, unless you can locate an auxiliary genstart unit from that era. You would also need a SW remote in order to program the units.
Allan

Allan Sindelar
[email protected]
NABCEP Certified Photovoltaic Installer
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Positive Energy, Inc.
3201 Calle Marie
Santa Fe, New Mexico 87507
505 424-1112
www.positiveenergysolar.com




On 7/28/2011 12:47 PM, William Miller wrote:
boB:

I'd like to run the inverters in the normal fashion with generator input (no PV):  (I'd thought these were SW inverters but they are PS series).

1. The inverters power 120 only loads (shared neutral on two feeders) so the inverters need to be stacked.
2. When the batteries get low, the inverters start the generator.  The inverters transfer through from the generator power to the loads and charge batteries.

Can the PS pair do this with a three phase generator?   I am beginning to think not...

William


At 10:56 AM 7/28/2011, you wrote:


Do you just want to charge batteries  and are these regular  120VAC SWs ??   120/208 ??

If so, you should just be able to connect each  SW from neutral to hot. No stacking necessary.

A regular SW stacking cable won't work for delta connections because that assumes
the phases are going to be 180 degrees (120/240) and not 120 degrees as  for 208V delta.

There was a 3 phase version of the SWs which required a separate 3-way cable and
different software in the SW itself.

boB




On Thu, Jul 28, 2011 at 12:23 AM, William Miller <[email protected]> wrote:
Friends:

Is there any way to connect two SW series inverters to two phases of a three phase generator?  It seems to me that one could connect three SW inverters with the right stacking cable (or am I confusing Outback inverters with the hub jumper set properly).

Any input is appreciated.

Thanks,

William

William Miller
Miller Solar
Voice :805-438-5600
email: [email protected]
http://millersolar.com
License No. C-10-773985
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

No virus found in this message.
Checked by AVG - www.avg.com
Version: 10.0.1390 / Virus Database: 1518/3793 - Release Date: 07/28/11

William Miller
Miller Solar
Voice :805-438-5600
email: [email protected]
http://millersolar.com
License No. C-10-773985

_______________________________________________ List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to