William,
Just a minor note: if I recall, the PS model was the first to
eliminate the generator autostart function and auxiliary relays from
the unit. It also eliminated the digital display and control panel.
It was intended as a low-cost "base model" of the SW series (I heard
some installers that the initials stood for Pile of ...). So I don't
think that these units can start the generator, unless you can
locate an auxiliary genstart unit from that era. You would also need
a SW remote in order to program the units.
Allan
Allan Sindelar
[email protected]
NABCEP Certified Photovoltaic
Installer
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Positive Energy, Inc.
3201 Calle Marie
Santa Fe, New Mexico 87507
505 424-1112
www.positiveenergysolar.com
On 7/28/2011 12:47 PM, William Miller wrote:
boB:
I'd like to run the inverters in the normal fashion with
generator input
(no PV): (I'd thought these were SW inverters but they are PS
series).
1. The inverters power 120 only loads (shared neutral on two
feeders) so
the inverters need to be stacked.
2. When the batteries get low, the inverters start the
generator.
The inverters transfer through from the generator power to the
loads and
charge batteries.
Can the PS pair do this with a three phase generator? I am
beginning to think not...
William
At 10:56 AM 7/28/2011, you wrote:
Do you
just want to charge
batteries and are these regular 120VAC SWs ??
120/208 ??
If so, you should just be able to connect each SW from
neutral to
hot. No stacking necessary.
A regular SW stacking cable won't work for delta connections
because that
assumes
the phases are going to be 180 degrees (120/240) and not 120
degrees
as for 208V delta.
There was a 3 phase version of the SWs which required a
separate 3-way
cable and
different software in the SW itself.
boB
On
Thu, Jul 28, 2011 at 12:23 AM,
William Miller
<[email protected]>
wrote:
- Friends:
- Is there any way to connect two SW series inverters to
two phases of
a three phase generator? It seems to me that one could
connect
three SW inverters with the right stacking cable (or am I
confusing
Outback inverters with the hub jumper set properly).
- Any input is appreciated.
- Thanks,
- William
- William Miller
- Miller Solar
- Voice :805-438-5600
- email:
[email protected]
- http://millersolar.com
- License No. C-10-773985
_______________________________________________
List sponsored by Home Power magazine
List Address: [email protected]
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
No virus found in this message.
Checked by AVG - www.avg.com
Version: 10.0.1390 / Virus Database: 1518/3793 - Release Date:
07/28/11
William Miller
Miller Solar
Voice :805-438-5600
email: [email protected]
http://millersolar.com
License No. C-10-773985
_______________________________________________
List sponsored by Home Power magazine
List Address: [email protected]
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
|
_______________________________________________
List sponsored by Home Power magazine
List Address: [email protected]
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org