I think 690.47 C 3 covers this in the new 2011 code. The info notes 1 & 2 also yield more clarification. As always confusion reins until we get some actual interpretation from Bill Brooks or John Wiles, as all of this was completely rewritten. Feel free to correct me, any and everyone, but this is my humble interpretation: The E-panel provides the required combined AC & DC grounding busbar (in note 1) Note 2 says you can use the existing premises grounding system, and C(3) says the AC EGC can be combined with the DC GEC and run back to the premises AC grounding busbar in the same conduit as your AC conductors. I think the main thing to check here is that you have properly sized the single combined conductor (AC EGC/ DC GEC) and that it is unspliced from the E panel to the main AC grounding busbar, and finally, that the existing AC GEC runs directly from that busbar to the grounding electrode. Its pretty clear IMHO that you don't need to run a separate GEC all the way back to the grounding electrode (unless you're not on 2011 code?)

BTW, I usually sink a supplemental ground rod direct from the E-panel for lightning protection ( and to satisfy 2008 code) but my read is that is no longer required by 2011 code as 690.47 D was deleted. I love how some folks act like you're going to burn the place down if you don't absolutely follow current code, and a couple of years later the code completely changes its mind, again, and again.....:)

Ray Walters


On 9/6/2011 1:59 PM, Aaron Mandelkorn wrote:
Wrenches,

Just installed a Magnum MS-PAE battery based system on an E-Panel distribution box and my inspector seems to have an issue with the grounding. He is saying that I must run an additional GEC down to the ground rod because I am dealing with two separate grounding systems. The DC and AC side of the grounding system shares the same ground buss bar in the E-Panel so why wouldn't a single GEC down to the ground rod suffice? The buss bar is where the two systems get grounded together rather than at the rod. The inspector is telling me to either dig up the rod and run an additional GEC down to it or connect the additional GEC to the existing with an irreversible splice. Am I missing something here? This requirement just seem redundant and wasteful. If I do have to make the correction I will be going with the splicing option. Some advise on irreversible splices would also be greatly appreciated. I can't seem to source them locally and have never used them before. Thanks for any help.


Aaron Mandelkorn
NABCEP Certified PV Installer

Renewable Energy Outfitters
(970)596-3744
[email protected] <mailto:[email protected]>
www.reosolar.com <http://www.reosolar.com>









_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options&  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules&  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to