I think 690.47 C 3 covers this in the new 2011 code. The info notes 1 &
2 also yield more clarification. As always confusion reins until we get
some actual interpretation from Bill Brooks or John Wiles, as all of
this was completely rewritten. Feel free to correct me, any and
everyone, but this is my humble interpretation:
The E-panel provides the required combined AC & DC grounding busbar (in
note 1) Note 2 says you can use the existing premises grounding system,
and C(3) says the AC EGC can be combined with the DC GEC and run back to
the premises AC grounding busbar in the same conduit as your AC conductors.
I think the main thing to check here is that you have properly sized the
single combined conductor (AC EGC/ DC GEC) and that it is unspliced
from the E panel to the main AC grounding busbar, and finally, that the
existing AC GEC runs directly from that busbar to the grounding electrode.
Its pretty clear IMHO that you don't need to run a separate GEC all the
way back to the grounding electrode (unless you're not on 2011 code?)
BTW, I usually sink a supplemental ground rod direct from the E-panel
for lightning protection ( and to satisfy 2008 code) but my read is that
is no longer required by 2011 code as 690.47 D was deleted.
I love how some folks act like you're going to burn the place down if
you don't absolutely follow current code, and a couple of years later
the code completely changes its mind, again, and again.....:)
Ray Walters
On 9/6/2011 1:59 PM, Aaron Mandelkorn wrote:
Wrenches,
Just installed a Magnum MS-PAE battery based system on an E-Panel
distribution box and my inspector seems to have an issue with the
grounding. He is saying that I must run an additional GEC down to the
ground rod because I am dealing with two separate grounding systems.
The DC and AC side of the grounding system shares the same ground
buss bar in the E-Panel so why wouldn't a single GEC down to the
ground rod suffice? The buss bar is where the two systems get
grounded together rather than at the rod. The inspector is telling me
to either dig up the rod and run an additional GEC down to it or
connect the additional GEC to the existing with an irreversible
splice. Am I missing something here? This requirement just seem
redundant and wasteful. If I do have to make the correction I will be
going with the splicing option. Some advise on irreversible splices
would also be greatly appreciated. I can't seem to source them
locally and have never used them before. Thanks for any help.
Aaron Mandelkorn
NABCEP Certified PV Installer
Renewable Energy Outfitters
(970)596-3744
[email protected] <mailto:[email protected]>
www.reosolar.com <http://www.reosolar.com>
_______________________________________________
List sponsored by Home Power magazine
List Address: [email protected]
Options& settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules& etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Home Power magazine
List Address: [email protected]
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org