Where in the NEC is the requirement for the GTI interface?

----- Original Message ----- From: "Kirk Herander" <[email protected]>
To: "'RE-wrenches'" <[email protected]>
Sent: Sunday, November 20, 2011 3:33 AM
Subject: Re: [RE-wrenches] Convert Grid Tie SW4048 to Backup System;Add New Inverter, AC Coupled


PS - Richard, does it have a Trace / Xantrex GTI interface installed? If
not, it's not code-legal to be tied to the grid anyway. Get rid of the 4048
whatever you do.

Kirk Herander
VT Solar, LLC
dba Vermont Solar Engineering
NABCEPTM Certified installer Charter Member
NYSERDA-eligible Installer
VT RE Incentive Program Partner


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Richard L
Ratico
Sent: Friday, November 18, 2011 6:53 PM
To: [email protected]
Subject: Re: [RE-wrenches] Convert Grid Tie SW4048 to Backup System; Add New
Inverter, AC Coupled

Jay, Marv, Chris, Ray, Joel & Maverick,

Thanks tremendously for your input. Each of you provided interesting
suggestions, all of which I find thought provoking and helpful. I greatly
appreciate your taking the time to share your experience.

Dick
Solarwind Electric


--- You wrote:
We redid one in a very similar situation recently. In that case the
customer wanted super backup and so we put in Grid tie Outbacks and a
new battery bank, added modules, and kept the SWs as battery chargers
from the generator. He had the option with bypass switches to use the
SWs, if the Outbacks went out. This guy wanted a "keep the power going,
no matter what" system, but I can't claim that was optimal.  The right
answer depends on what the customer wants.
I probably wouldn't trash everything though as Jay suggested, since the
existing modules are already racked and wired. (unless it's a bogus
install, then yep, salvage it all)
You could probably easily rewire the parallel 48 v sets of modules all
in series in 15 minutes in the combiner box to get the voltage up, and
use a small GT only inverter, too. I guess it would also depend on how
close the 2 different types of modules are in voltage or current, but it
doesn't have to be perfect; as these were modules headed to the scrap
heap otherwise.
In honor of modules that are well installed and still performing
correctly, I do try and reuse them. Being able to brag: "these have been
working for 30 years..." is great for the solar industry as a whole, but
only if it makes sense.

Ray

On 11/17/2011 5:51 PM, jay peltz wrote:
HI Richard,

I'll chime in, although you won't like it.

Dump the system and start over with a new battery less system and a genny
as
back up.

Told you, you wouldn't like it.

The SW parts are basically gone and it was a terrible  grid tied inverter
anyway.
The modules are usable but why at $1.5 watt keep them?
Client doesn't want MX, so that means no batteries.

You'll need a genny as back up anyway for long power outages during
storms, so
get a natural gas/propane unit as back up instead of batteries.

OK you asked,

jay

peltz power
On Nov 17, 2011, at 4:03 PM, Richard L Ratico wrote:

Hi Wrenches,

This is a repost. No replies the first time, so I'm trying one last time.

I may be "adopting" an eleven year old, Y2K, grid tie with battery
back-up
system. It consists of 12 - Astro-Power 120 modules, installed in 2000,
12 -
Evergreen  EC-110 modules installed in 2004, only one MX60, which
controls
BOTH
sub-arrays, one SW4048 in SELL mode through a dedicated load sub-panel.
Existing, seven year old battery is shot (8-Trojan L-16). Initial bank of
unknown batteries was replaced after only four years.

Recent long, nearby, utility outages have the client requesting a
proposal to
include a new back-up generator and to restore the system selling to the
grid.
Client may decide go straight grid tie to eliminate the batteries. They
have
found the maintenance to be a hassle.

My thoughts so far:

1)To take advantage of most of the existing hardware, I wonder if it
makes
sense
to try to improve the system efficiency by relegating the SW to a manual
back-up
mode only, where, say, by means of a timer controlling grid availability
through
AC1, it would only charge a smaller battery bank once a week. The battery
bank
would be small,
a single string of either, sealed gel units or T-105s with the new Trojan
watering system.
2) Provide new grid-tie inverter/s (appropriate string type or Enphase
190s)
to
handle the net metering.
3) Provide a way to AC couple the new inverter/s to the SW in the event
of an
outage.
4) Provide a new Honda 3000 inverter type generator connected to AC2 in
the
SW.
5)Provide a way to lockout the grid tie inverter/s when the generator is
operating.

Any thoughts or suggestions would be greatly appreciated.

Thanks in advance,

Dick Ratico
Solarwind Electric
Bradford, VT
--- end of quote ---
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to