Wrenches,

I answered Richard off-list, but other wrenches may find this information about 
old SW4048s and batteries useful.

The SW4048 is a solid machine. We've been using one since 1998 and have sold 
hundreds of them for both on and off grid systems. We would leave what's 
working alone and replace and expand the battery bank to meet the client's 
expected grid outage hours. Our system has only 4 kWh of sealed batteries 
because we live in an area that gets almost no power outages and did not want 
to bother watering batteries. See info and wiring diagram at 
http://www.solarsolar.com/oursys.html 

On the other hand, one of our clients in Malibu on the grid had an off-grid 5 
kW PV system for backup power with 75 kWh of IBE flooded lead-acid batteries (2 
parallel strings of 24 each 2-volt cells). We installed the system in 1993 but 
no one maintained the batteries properly. So in 1996 the dead IBE battery bank 
was replaced with a maintenance-free, sealed Absolyte battery bank that only 
lasted 4 years because of 40 F to 90 F temperature swings in the equipment 
room. A few years ago, we upgraded the system with a 31 kW array, 6 Sunny Boys, 
2 Sunny Islands, and went back to a new set of 75 kWh of IBE cells like before. 
Now the batteries are inspected and watered every 2 to 6 months. We are still 
determining the right service period.

I have learned to buy good batteries, install them where the temperature stays 
60 to 70 degrees F. as much as possible, inspect and water flooded batteries at 
least 2 times per year. All things being equal, sealed lead-calcium batteries 
cost twice as much and last half as long as flooded lead-antimony batteries. 
Most importantly, batteries are electro-chemical things just like living 
organisms. Keep them clean, fed (fully charged as much as possible), properly 
watered, at 70 degrees F, don't over-work them (deeply discharged without fully 
charging promptly), and they will last 6 to 8 years easily and often 12 years 
before old-age (high self-discharge) sets in. Battery bank owners that take 
care of themselves, their families, their animals, and their vehicles carry 
those good habits over to taking care of their battery banks. It's sad but true 
that people who are unhealthy and have vehicle problems all the time almost 
always have battery problems.

Best regards,
Joel Davidson



  ----- Original Message ----- 
  From: Allan Sindelar 
  To: [email protected] 
  Sent: Sunday, November 20, 2011 8:21 AM
  Subject: Re: [RE-wrenches] Convert Grid Tie SW4048 to Backup System; Add New 
Inverter, AC Coupled


  Kirk,
  I think there are a couple of subtleties that you're missing in your post. 
All of the SW series that we installed in grid-tied mode prior to Trace/Xantrex 
losing its 1741 listing - mostly Y2K installations - are still in use legally, 
as they were grandfathered in. Once Xantrex lost its listing and went to the 
GTI models (firmware rev. 4.10 and above), only with a GTI were they 1741, and 
the earlier inverters couldn't be retrofit.

  So if Richard's customer's SW4048 is pre-GTI and is currently legitimately 
utility-interactive, it could be argued that it's grandfathered in. Of course, 
I'd avoid arguing anything that esoteric with any governing body. 

  But it's a moot issue anyway. Reviewing the other Wrenches' suggestions, none 
advised continuing to use the SW as an interactive inverter, but only as a 
charging source for a battery bank. One Wrench suggested putting the SW's AC 
input on a weekly timer, which is a good idea. Jay is correct that the SW was a 
terrible inverter for grid-tie. One primary weakness of the SW series was that 
as long as the grid was up, it tried to maintain float voltage to the batteries 
continuously (this was the "lack of silent sell" issue). This brought overall 
sell efficiency down to around 55%, as I recall, rather than the 93+% 
efficiency of today's inverters. But if the inverter is only being used as a 
charging source, it's not selling and thus neither the poor efficiency nor the 
lack of a GTI is relevant.

  Personally, I wouldn't get rid of the SW if the customer wants battery 
backup. The inverters have proven generally reliable, and this one is likely to 
last for decades as an occasional battery charger. Plus it's already paid for, 
and does a good job as both a battery charger and a backup inverter during 
outages. I'd use sealed batteries to deal with the customer's maintenance 
concerns. The Honda 3000i is a good choice at sea level, as the SW can 
hard-limit the AC amp draw from an undersized generator and avoid overloading 
it (and nuisance-tripping its output breaker). But note that the SW can take up 
to about 5,200 watts from an AC source, and sealed batteries prefer high 
charging C/rates, so you might want to use a generator of around 6kW (at 120V) 
instead for better efficiency and less runtime.

  Good thing Richard reposted - the second time got a bunch of us responding. 
Kinda fun...

  Allan


  Allan Sindelar
  [email protected]
  NABCEP Certified Photovoltaic Installer
  NABCEP Certified Technical Sales Professional
  New Mexico EE98J Journeyman Electrician
  Positive Energy, Inc.
  3201 Calle Marie
  Santa Fe, New Mexico 87507
  505 424-1112
  www.positiveenergysolar.com 






  On 11/20/2011 4:33 AM, Kirk Herander wrote: 
PS - Richard, does it have a Trace / Xantrex GTI interface installed? If
not, it's not code-legal to be tied to the grid anyway. Get rid of the 4048
whatever you do.

Kirk Herander
VT Solar, LLC
dba Vermont Solar Engineering
NABCEPTM Certified installer Charter Member
NYSERDA-eligible Installer
VT RE Incentive Program Partner


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Richard L
Ratico
Sent: Friday, November 18, 2011 6:53 PM
To: [email protected]
Subject: Re: [RE-wrenches] Convert Grid Tie SW4048 to Backup System; Add New
Inverter, AC Coupled

Jay, Marv, Chris, Ray, Joel & Maverick,

Thanks tremendously for your input. Each of you provided interesting
suggestions, all of which I find thought provoking and helpful. I greatly
appreciate your taking the time to share your experience.

Dick
Solarwind Electric


--- You wrote:
We redid one in a very similar situation recently. In that case the 
customer wanted super backup and so we put in Grid tie Outbacks and a 
new battery bank, added modules, and kept the SWs as battery chargers 
from the generator. He had the option with bypass switches to use the 
SWs, if the Outbacks went out. This guy wanted a "keep the power going, 
no matter what" system, but I can't claim that was optimal.  The right 
answer depends on what the customer wants.
I probably wouldn't trash everything though as Jay suggested, since the 
existing modules are already racked and wired. (unless it's a bogus 
install, then yep, salvage it all)
You could probably easily rewire the parallel 48 v sets of modules all 
in series in 15 minutes in the combiner box to get the voltage up, and 
use a small GT only inverter, too. I guess it would also depend on how 
close the 2 different types of modules are in voltage or current, but it 
doesn't have to be perfect; as these were modules headed to the scrap 
heap otherwise.
In honor of modules that are well installed and still performing 
correctly, I do try and reuse them. Being able to brag: "these have been 
working for 30 years..." is great for the solar industry as a whole, but 
only if it makes sense.

Ray

On 11/17/2011 5:51 PM, jay peltz wrote:
HI Richard,

I'll chime in, although you won't like it.

Dump the system and start over with a new battery less system and a genny
as
back up.
Told you, you wouldn't like it.

The SW parts are basically gone and it was a terrible  grid tied inverter
anyway.
The modules are usable but why at $1.5 watt keep them?
Client doesn't want MX, so that means no batteries.

You'll need a genny as back up anyway for long power outages during
storms, so
get a natural gas/propane unit as back up instead of batteries.
OK you asked,

jay

peltz power
On Nov 17, 2011, at 4:03 PM, Richard L Ratico wrote:

Hi Wrenches,

This is a repost. No replies the first time, so I'm trying one last time.

I may be "adopting" an eleven year old, Y2K, grid tie with battery
back-up
system. It consists of 12 - Astro-Power 120 modules, installed in 2000,
12 -
Evergreen  EC-110 modules installed in 2004, only one MX60, which
controls
BOTH
sub-arrays, one SW4048 in SELL mode through a dedicated load sub-panel.
Existing, seven year old battery is shot (8-Trojan L-16). Initial bank of
unknown batteries was replaced after only four years.

Recent long, nearby, utility outages have the client requesting a
proposal to
include a new back-up generator and to restore the system selling to the
grid.
Client may decide go straight grid tie to eliminate the batteries. They
have
found the maintenance to be a hassle.

My thoughts so far:

1)To take advantage of most of the existing hardware, I wonder if it
makes
sense
to try to improve the system efficiency by relegating the SW to a manual
back-up
mode only, where, say, by means of a timer controlling grid availability
through
AC1, it would only charge a smaller battery bank once a week. The battery
bank
would be small,
a single string of either, sealed gel units or T-105s with the new Trojan
watering system.
2) Provide new grid-tie inverter/s (appropriate string type or Enphase
190s)
to
handle the net metering.
3) Provide a way to AC couple the new inverter/s to the SW in the event
of an
outage.
4) Provide a new Honda 3000 inverter type generator connected to AC2 in
the
SW.
5)Provide a way to lockout the grid tie inverter/s when the generator is
operating.

Any thoughts or suggestions would be greatly appreciated.

Thanks in advance,

Dick Ratico
Solarwind Electric
Bradford, VT
--- end of quote ---
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




------------------------------------------------------------------------------


  _______________________________________________
  List sponsored by Home Power magazine

  List Address: [email protected]

  Options & settings:
  http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

  List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

  List rules & etiquette:
  www.re-wrenches.org/etiquette.htm

  Check out participant bios:
  www.members.re-wrenches.org

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to