I would run a wire, I have seen metallic conduit used as ground come apart in buildings. At that point we know where the ground (or at least the connection goes..)
I doubt that it makes a difference whether it is single or 3 phase. But there are lots of people on the list with more 3 phase experience than I have. Later, Bob Ellison From: [email protected] [mailto:[email protected]] On Behalf Of Allen Frishman Sent: Tuesday, December 06, 2011 3:30 AM To: RE-wrenches Subject: [RE-wrenches] GEC and EGC Advice Fellow Wrenchers, I know this topic has come up before and I have a understanding but I am looking for best practices advice. When installing a 50KW or larger 3 phase 208V (WYE Service) Inverter on a roof do you run your Grounding Electrode Conductor in a separate conduit from the 3 hots, and the Equipment Grounding Conductor or do you run it all in the same conduit together. My thought is to run it all in the same conduit and utilize the metalic conduit as the Equipment Ground instead of running a actual conductor for the EGC. All feedback is appreciated. Al Frishman AeonSolar (917) 699-6641 <tel:%28917%29%20699-6641> - cell (888) 460-2867 <tel:%28888%29%20460-2867> www.aeonsolar.com <http://www.aeonsolar.com/>
_______________________________________________ List sponsored by Home Power magazine List Address: [email protected] Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org