I'd avoid using the metal conduit as the only bond in your equipment grounding 
from the roof down to other equipment. If the GEC is bonded to the rest of the 
equipment grounding system at a point on the ground, then of course it can 
double as the EGC. Otherwise, if you don't want to use a separate EGC 
conductor, better to split-bolt or splice by another means from the GEC once 
you're on the ground and run an EGC back to busbar in the equipment grounding 
system.

Jeffrey Quackenbush
NABCEP-certified PV installer
Ninja Solar


________________________________
 From: Allen Frishman <[email protected]>
To: RE-wrenches <[email protected]> 
Sent: Tuesday, December 6, 2011 1:59 PM
Subject: [RE-wrenches] GEC and EGC Advice
 

Fellow Wrenchers,
I know this topic has come up before and I have a understanding but I am 
looking for best practices advice.

When installing a 50KW or larger 3 phase 208V (WYE Service) Inverter on a roof 
do you run your Grounding Electrode Conductor in a separate conduit from the 3 
hots, and the Equipment Grounding Conductor or do you run it all in the same 
conduit together.

My thought is to run it all in the same conduit and utilize the metalic conduit 
as the Equipment Ground instead of running a actual conductor for the EGC.

All feedback is appreciated.

Al Frishman
AeonSolar
(917) 699-6641 - cell
(888) 460-2867
www.aeonsolar.com 

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to