The problem here is that the previous solar company used fairly long crimp lugs with heat shrink, which adds to the bending stress. Also, its impossible to work in a Flex box with 2 inverters, 2 FM80s, and the new triple shunt flex meter, and not be moving those #4 wires around to say, land the 4/0 battery cables. I personally think that UL dropped the ball and should not have let that flimsy mount pass, or it should be listed for flex cable only. I did plenty of prebending, but there just is no such thing as unstressed, when landing a #4 or larger THHN. Any other lug, in most other UL listed breaker boxes, is securely mounted. When was the last time a lug snapped off in a Square D load center? The breaker snaps out before it breaks. Panel mounted breakers have to be sturdier than their snap in cousins, not less. This is more than just an install PITA, it is a dangerous situation, as the wire that snaps off could be hot from the battery, or from the array. I also think its possible that the breaker could break later after a few heat/ cool cycles, even if it didn't break initially . Loose, energized wires inside a load center seems like a very bad idea. As Kent pointed out, as soon as the tab bends up, it's game over. I was considering a zip tie to secure the cable to the breaker, but the bottom line is we shouldn't have to modify (and probably void the listing of) UL listed breakers in the field. If I was doing something weird like landing a 1/0 cable, I could see it was my problem. But you can't put less than a #4 on an 80 amp breaker last time I checked, so the breaker should be able to hold a #4 with some normal bending and jostling that installations cause.

Ray

On 12/17/2011 8:39 AM, jay peltz wrote:
Hi Ray,

The only way I work on them with larger wire is with the breaker mounted in the 
mounting plate and the mounting plate screwed in, then I bring the wire pre 
bent/unstressed to the post.


Jay

Peltz Power



Sent from my iPad

On Dec 16, 2011, at 9:14 PM, Ray Walters<[email protected]>  wrote:

Hi Folks;

Anybody else having trouble with the small Outback DC breakers snapping posts 
off?  I just took over a GTB job from another reputable GT solar company, after 
they twisted off a post on an 80 amp breaker with #4 wire.  I know those are 
delicate breakers with low torque limits when tightening, so I took over.   I 
dropped the breaker mounting plate, so that I could work on the breakers, and 
then I saw how weak the posts looked, just bending the #4 wires gently still 
cause another breaker post to stress, and then break.  I worked as gently as I 
could, but I could not even get the plate back in position without damage.
In my opinion, those breakers are suspect with #6 wire, and they just can't 
handle #4 or larger, unless maybe it was a flex type.
The old medium body Heinemans  (125 amp) used to come in an 80 amp variety, 
which was much sturdier.   Is there an adapter that would let me use that type 
of breaker on the Flexware box?


Ray Walters





_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options&  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules&  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options&  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules&  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org





_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to