In Texas, for the Oncor Energy TDSP (transmission & distribution service provider) interconnection agreement, an outside disconnect* is required. If a PV installation is submitted to Oncor for a rebate, they also require the inclusion of PV REC (renewable energy credit) meter, but do not require it to be located outdoors, or in close proximity to their own revenue meter. The meter must be one listed on the CEC approved list.

   /* Oncor's interconnection requirements specify a manual disconnect
   device. The disconnect must have a visual break that is appropriate
   to the voltage level, be accessible to utility personnel, and
   capable of being locked in the open position. Oncor requests that
   this visible AC disconnect be located on an exterior wall and within
   ten feet of the Oncor meter. If your visible AC disconnect is more
   than ten feet from the Oncor meter, then Oncor will request a site
   directory placard be installed on customer equipment beside the
   Oncor meter or where there is only an Oncor meter then on the Oncor
   meter base indicating the location of the visible AC disconnect./

Oncor does not require a disconnect on both sides of the PV REC meter, but your inspecting AHJ might.


Regards,

Gary Willett, PE


On 1/24/2012 08:52, mac Lewis wrote:
Here in Xcel territory in Colorado, we are required to cold-sequence the solar production meter. These disconnects have to be utility accessible and adjacent to the production meter itself. I believe this is only a utility requirement, not a code requirement. This seems to be unneeded redundancy, because the inverter side will shut down, once the line side is deenergized.

Mac Lewis

On Tue, Jan 24, 2012 at 7:14 AM, Allen Frishman <[email protected] <mailto:[email protected]>> wrote:

    Wrencher's,
    I am having a good debate with a fellow solar installer regarding
    an NEC requirement to isolate a meter between two disconnecting
    means adjacent to the meter when grid connecting via a tap.   My
    thought is that if we have a load center with breakers to combine
    multiple inverters on the roof, the PV meter can be located in the
    basement between the roof load center and a fused disconnect
    adjacent to the tap with no need for a disconnect next to the
    meter on the load center side of the meter.  Can anyone reference
    a section in the code that requires a disconnecting means adjacent
    to both sides of the meter?  The meter I am referencing simply
    records the total kWh's of the solar system as required by the
    State incentive program.

    All feedback is appreciated.

    /Al Frishman/
    AeonSolar

    /(917) 699-6641 <tel:%28917%29%20699-6641> - cell/
    /(888) 460-2867 <tel:%28888%29%20460-2867>/
    /www.aeonsolar.com <http://www.aeonsolar.com/>/



    _______________________________________________
    List sponsored by Home Power magazine

    List Address: [email protected]
    <mailto:[email protected]>

    Options & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    List-Archive:
    http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm
    <http://www.re-wrenches.org/etiquette.htm>

    Check out participant bios:
    www.members.re-wrenches.org <http://www.members.re-wrenches.org>





--



Mac Lewis

*

"Yo solo sé que no sé nada." -Sócrates

*


_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options&  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules&  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to