Darryl:

I respectfully disagree with the use of the bonding screws. In general, there are two panels that require bonding: The service and a separately derived system. The service needs a neutral-ground bond screw but the second panel is a sub-panel and must have an isolated neutral.

William

PS: When considering how to bond and feed neutrals to a critical loads panel, think about how the neutrals are connected in the inverter. Unless the inverter is a "mobile" unit, the in and out neutrals are connected together in the inverter. When using an integrated BOS AC cabinet, only one neutral is required. Therefore one neutral buss is technically all that is needed for the described scenario. Your inspector may very likely not be comfortable seeing no neutral buss in one panel. If required, you can feed the new panel neutral from the inverter or from the service panel. With proper low impedance connections, they are all the same potential and complete the circuit path back to the service transformer, the ultimate duty for a neutral buss.

Wm


At 06:42 AM 5/8/2012, Darryl Thayer wrote:
Locally if you have two service panels next to each other, inspectors want both bonded and grounded, by allowing a bonding jumper from panel one to panel 2, and both panesl use the bonding screw, and both have to have a neutral bus.

From: Corey Shalanski <[email protected]>
To: [email protected]
Sent: Tuesday, May 8, 2012 6:51 AM
Subject: [RE-wrenches] Critical Loads Panel Wiring

Wrenches,

Batt backup system: When placing a critical loads panel directly adjacent to the main service panel (in the next stud bay), must the neutral and ground conductors be pulled into the new subpanel? or can only the hots be pulled? Any Code references would be appreciated.

--
Corey Shalanski
Joule Energy
New Orleans, LA
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to