I think that technically, the combiner panel is not compliant if the possible feeds from various sources exceed 120% of the busbar rating.

Inspectors have been reasonable on this issue, as it can be done safely. The solution, if the AHJ won't accept a small combiner panel is to use a panel with a higher busbar rating and a main breaker small enough so that the combination of the main and solar feeds does not exceed 120% of the busbar rating. It can result in some awkwardly large and technically unnecessary boxes.


At 07:29 AM 6/27/2012, you wrote:
If the combining panel is next to the main panel, can you use a Main Lug panel as the combining panel or does it need a main breaker? I'm not sure what the purpose of the main breaker would be if there are no loads.

--
Chris Mason
President, Comet Systems Ltd
<http://www.cometenergysystems.com>www.cometenergysystems.com

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Drake Chamberlin
ATHENS ELECTRIC LLC
OH License 44810
CO license 3773
NABCEP Certified PV
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to