i have always used the good old e-meter/link 10. i manually program the charge 
efficiency at 99% (why won't the manufactures allow a 100% setting?). the 
problem is that 1% error... since the meter treats charge different than 
discharge.

 
the old e-meters seemed to handle this fine... but the newer ones (before they 
discontinued them) had a problem. with the shunt shorted (see time delay relay 
notes below), the meter read .4 amps of current flow, so obviously an 
accumulating error happens with these.
 
i am about to replace one of these defective link 10's with a trace tm-500, 
which another local installer said works ok in this application (when manually 
set to 99% charge efficiency). i will report back to the list about the status 
of this "fix". but, even if it does work, as the grid reliability decreases in 
the coming years... when the grid is down, the meter will incorrectly report 
the battery soc, since it is obviously not at 99%. i had considered a 
rube-goldberg system where the meter would left programmed in the default 
setting to automatically calculate charge efficiency and a time delay relay 
would short out the shunt when the grid was up to keep the meter reading at 
100%. if the tm-500 doesn't work, i will try this. either way, i will report 
back to the group as i know this is a vexing problem for many people who do 
gtwbb systems.
 
as to the grid outage alarm, with the inverter out at the service disconnect, 
did you run a long, large gauge, twisted pair cable to the amp-hour meter in 
the house? do you have 2 extra conductors for an alarm? if not, how about an 
x-10 (or similar) remote switch at the grid disconnect to 'talk' to a light or 
alarm in the house?
 
todd
 




 Incidentally, your comment about an amp-hour meter brings another       
question: a traditional amp-hour meter, like a TriMetric       2020,doesn't 
work well in GTWB situations, as the charged       parameters are seldom met 
absent a grid outage, and thus the       charge efficiency error can accumulate 
over time and lead to false       readings. What do you use, Todd, or if you 
use a traditional       amp-hour meter, how do you program it to fool it into 
maintaining       accuracy in a system that always sits in float?
 Allan




Allan Sindelar
[mailto:[email protected]] [email protected]
NABCEP Certified Photovoltaic             Installer
 NABCEP Certified Technical Sales Professional
 New Mexico EE98J Journeyman Electrician
 Founder and Chief Technology Officer
Positive Energy, Inc.
 3209 Richards Lane (note new address)
 Santa Fe, New Mexico 87507
505 424-1112
[http://www.positiveenergysolar.com/] www.positiveenergysolar.com
 

On 8/9/2012 10:02 AM, [mailto:[email protected]] 
[email protected] wrote:
99% of the grid-ties i do           incorporate battery backup. when i am 
wiring a system into a           house, i usually put the amp hour meter in the 
kitchen and           only wire essential back up loads (water pump, 
communication,           refrigeration & basic lighting) into the system. this  
         design alerts the customer of when the grid is down and they           
need to go into 'conserve mode', and also eliminates power           robbing 
waste.
 
i am not sure why your customer           would want to have the whole house 
backed up? i try to leave a            couple of non essential, but noticeable 
circuits as 'grid           only'. if the house is already wired and changing a 
circuit is           not possible, you will need to somehow access a grid only  
         circuit (the ac input to the inverter) and put some kind of           
alarm on it. hardware stores sell battery powered lights that           come on 
when the power is off. one of these could be modified           with a sonalert 
(or other audible alarm) which would come on           to notify the customer 
to change their behavior.
 
todd
 
 
 
On Thursday, August 9, 2012           8:18am, "Allan Sindelar" 
[mailto:[email protected]] <[email protected]> said:


Wrenches,
 For a grid-tied-with-backup system that is still in the design           
stage, we have a customer request for a signal to let them           know when 
an outage occurs and they are running on backup           power, so that they 
may turn off unnecessary loads and "go           into backup consciousness". 
The problem is that the entire           home would be on backup, with the GTWB 
system tied into a           meter and main disconnect location away from the 
home, rather           than the more typical main panel/subpanel approach at 
the           home. Any relay-based alarm based on loss of grid AC would not    
       likely trigger, as the switchover is too quick. Any ideas for           
simple solutions, please?
 Allan

-- 
Allan                 Sindelar
[mailto:[email protected]] [email protected]
NABCEP Certified                 Photovoltaic Installer
 NABCEP Certified Technical Sales Professional
 New Mexico EE98J Journeyman Electrician
 Founder and Chief Technology Officer
Positive Energy, Inc.
 3209 Richards Lane (note new address)
 Santa Fe, New Mexico 87507
505 424-1112
[http://www.positiveenergysolar.com/] www.positiveenergysolar.com
 




 Sent from Finest Planet WebMail.



Sent from Finest Planet WebMail.


Sent from Finest Planet WebMail.
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to