See 690.13. There must be a means to disconnect all conductors of a PV system. If it is a normally grounded array you are not allowed to put a switch in the grounded conductor, except .... for circumstances added in the 2011 code.
Kent Osterberg
Blue Mountain Solar, Inc.
www.bluemountainsolar.com
t: 541-568-4882
On 9/14/2012 4:39 PM, Bob Clark wrote:

Wrenches:

 

A local utility person has suggested that both the positive and negative conductors from a solar array should be disconnected.

 

Disconnect both or not?  2008 NEC supporting citation please.

 

Thanks for your response.

 

Bob Clark

SolarWind Energy Systems, LLC

P.O. Box 1234

Okanogan, WA 98840

(509) 826-1259

 

Although no trees were killed in the sending of this message, a large number of electrons were terribly inconvenienced.