Most often it is the negative wire that is grounded, but not all of the time. Whichever is grounded should have white or light gray insulation and it should have a mechanical connector or bus bar connection in the disconnect switch so that the grounded conductor can be opened for maintenance. While that is what the code says, I don't feel a small array is any more dangerous if both conductors are switched. Quite the opposite: the array is "probably" safer if both conductors are open.

For an ungrounded array, which will probably become more common as equipment is designed to operate that way, both conductors are supposed to be switched in the disconnect. In that case there shouldn't be any white wire going to the PV array.

Kent Osterberg
Blue Mountain Solar, Inc.
www.bluemountainsolar.com
t: 541-568-4882


On 9/14/2012 6:46 PM, Bob Clark wrote:

Kent:

 

In a normally grounded array, the grounded conductor is the negative conductor, right?  So, no disconnecting the negative conductor.  It should go straight through the DC disconnect and on to the inverter.  Correct?

 

Bob Clark

SolarWind Energy Systems, LLC

P.O. Box 1234

Okanogan, WA 98840

(509) 826-1259

 

Although no trees were killed in the sending of this message, a large number of electrons were terribly inconvenienced.

cid:822514723@19022009-0502

 

From: [email protected] [mailto:[email protected]] On Behalf Of Kent Osterberg
Sent: Friday, September 14, 2012 5:00 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Disconnect BOTH positive and negative conductors from array?!?

 

See 690.13. There must be a means to disconnect all conductors of a PV system. If it is a normally grounded array you are not allowed to put a switch in the grounded conductor, except .... for circumstances added in the 2011 code.

Kent Osterberg
Blue Mountain Solar, Inc.
www.bluemountainsolar.com
t: 541-568-4882

On 9/14/2012 4:39 PM, Bob Clark wrote:

Wrenches:

 

A local utility person has suggested that both the positive and negative conductors from a solar array should be disconnected.

 

Disconnect both or not?  2008 NEC supporting citation please.

 

Thanks for your response.

 

Bob Clark

SolarWind Energy Systems, LLC

P.O. Box 1234

Okanogan, WA 98840

(509) 826-1259

 

Although no trees were killed in the sending of this message, a large number of electrons were terribly inconvenienced.

cid:822514723@19022009-0502

 


_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to