Well Steve, 
Let me wipe the egg off my face....It is right there on page 59 of Xantrex 
manual, version 975-0004-01-02 Rev D. "If the current exceeds 85 amps, the 
transistor switches are opened..." Upon further reading, it appears that all 
three controllers can handle 85 amps intermittently. I'm not surprised at that 
since I can't remember seeing a C-Series controller burned up like so many 
others I have encountered.

Thanks Steve for my continuing education. Are there ANY other non-MPPT 
controllers out there with a over-current protection?

Larry Crutcher
Starlight Solar Power Systems



On Oct 25, 2012, at 6:38 AM, Bell, Steve wrote:

The C-40 does (or at least did) have Electronic Overcurrent Protection. 
According to the C-40 manual if the current exceeds 63 amps  the overcurrent 
protection is activated.  The C-40 automatically resets the OCP every 10 
minutes until the problem is corrected or stops. The OCP can also be reset 
manually by holding the reset switch down for 5 seconds.
 
Steve
 
Steve Bell
Technical Support Specialist
 
SunWize Technologies, Inc.
#1 Sun Street
Stelle, IL  60919 USA
(815) 256-2222 ext. 23
[email protected]
www.sunwize.com